Discuss 16mm T+E and adiabatic equation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

rs250250

Evening all,
I have a question regarding calculation of CPC on a 16mm T+E and wondered if you could help at all.

I have done a board change and the supply is via a 16mm T+E. It appears the CPC is 6mm and therefore I did the adiabatic equation to confirm if the CPC is adequate.
The circuit is fed via 60A BS1361 type 2. The issue I have had is that BS1361 is no longer listed in appendix 3. Does any one know what table in appendix 3 should be used? Looking through the green book it appears that the equivalent would be BS88-3?

I therefore did the following calc. S = √ISq t/k
TN-S system
My Ze was 0.12ohms so fault current is 230/0.12=1916A
K value was 115 as cables bunched with other circuits (taken from table 54.3)
1916A squared = √3671056 x 0.1S disconnection time. (i assume due to the fault current and reference to table 3A1 it would be 0.1S) = 605.892/115 = 5.26mm CPC

Therefore 6mm would suffice.

If anyone can confirm or correct this I would be grateful. I still find the idea of using anything so small as uncomfortable, but if it complies then I am happy.

Many Thanks
 
you dont use Ze for the fault current calc in a adiabatic check , you use Zs , or in this case the Z at the DB.
and yes bs 88 is the "new" 1361
 
You need to obtain a copy of the pre-amendment Regulations, or look up on google for the time/current characteristics.
BS88-3 has replaced BS1361, but the time/current characteristics are different.
 
You need to obtain a copy of the pre-amendment Regulations, or look up on google for the time/current characteristics.
BS88-3 has replaced BS1361, but the time/current characteristics are different.
Spot on with that. It is essential you locate the time / current characteristics for the fuse installed as this may well be the difference between a satisfactory outcome or a non compliant supply requiring upgrading which another spark will gladly shoot you down on if he prooves your calculations were incorrect.
 

Reply to 16mm T+E and adiabatic equation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock