I have been asked to price for a db change in a flat above a veterinary centre that the nurses on call stay in. The supply to the whole building is a TN-S 2 phase. It has a 16mm main earth conductor, 25mm tails and 10mm's to services.
The flat above is supplied with a piece of 16mm T&E on a 60A switch fuse on a seperate credit meter to a wylex re-wirable board. Is the 6mm cpc in the 16mm T&E allowed if it is ok with the adiabatic equation? or does it have to be upgraded to 16mm for me to be allowed to fit the new db? As usual to route a new cpc is a pig of a job!
Any help much appreciated
 
no i dont think it would sufficce the earth conductor should be at least half the size of the line conductors 16/2=8 so therefore i wouldnt av thought the 6mm cpc wud do but i will stand corrected as usual:D
 
no i dont think it would sufficce the earth conductor should be at least half the size of the line conductors 16/2=8 so therefore i wouldnt av thought the 6mm cpc wud do but i will stand corrected as usual:D

No Mark, you definately cannot use half the line conductor size for your earth size with 16mm cable.

You either use 16mm earth or do the adiabatic equation, so Jimmer could use the 6mm intergral if the calculation allows.
 
i personally always use split concentric for sub mains, occasionally il use armoured, obviously u cnt use 8mm but i thought i read sum wer if it was bein used as a sub main the earthing conductor wud have to be greater than half that of the phase? not disagreein with u andy genuine intrested
 
Its the same size as the line conductor up to 16mm,
then it's 16mm up to I think 35mm ( I need to check this in the regs, it might be 50mm but I'm fairly certain it's 35mm)
Then 1/2 the size of the line conductor after that.
 
The minimum csa of the main earthing conductor must be determined by the adibiatic equation or selected from Table 54.7 543.1.1.
If the adibiatic equation is used, the minimum csa of the main earthing conductor must be 6mm 544.1.1.
 
I think it's a minimum of 10mm as Bugsy has said above. Table 4.1 in the osg. So looks like your running that separate single core earth cable for the new cu or let some other sod do it. :)
 
I think it's a minimum of 10mm as Bugsy has said above. Table 4.1 in the osg. So looks like your running that separate single core earth cable for the new cu or let some other sod do it. :)

Table 4.1 of the osg is for when the csa is not calculated as per 543.1.3 of the regs.
 

Reply to 16mm T&E sub-main question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
387
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
872
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock