Discuss 16mm T&E tails on 100amp fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
168
Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e.
I did nor remove the fuse carrier to check the actual fuse as it was sealed :rolleyes:

Anyhow my point is, ive already installed new circuit and have to issue an EIC, I will be writing in comments box write what I found and that it looks wrong. However looking forward what should I do about this. The customer wont be happy me turning off all the power; I told him to contact the people he bought the house from and raise the point.

Another thing I found includes a spur that don't switch off the load in garage that its labelled to do. Its not right is it, brand new house as well, and theres hundreds of them.
 
There is acceptable Ze, main earth at the board is single g/y 16mm, water and gas bonded with 10mm also.

Next thing I would worry about is did the cable run need RCD protection due to the nature of the install ?

The service fuse carrier is always marked 100A as the max rating of fuse. The fuse would need to be checked to ascertain if the tails need fusing down after it.
 
What is the FCU supposed to switch off in the garage?
 
Measure the PFC and then conduct the Adiabatic equation, to determine whether the conductors are under sized.

Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
 
Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.

I had one last week where Main fuse blew twice in a week .. was replaced by electric co. I thought maybe the cause was too much usage ... Took the Main Fuse ( no seal ) ... but alas it was a grey fuse with no writing on it !! so i was none the wiser .
 
Note on the cert stating you're unable to verify the size of the DNO fuse.

Not your place to start pulling fuses. You may contact the DNO to find out but they probably don't know either.
 
Note on the cert stating you're unable to verify the size of the DNO fuse.

Not your place to start pulling fuses. You may contact the DNO to find out but they probably don't know either.

Yes I will be doing that, lesson learnt today, check service head before any works done, not afterwards.
 
Next thing I would worry about is did the cable run need RCD protection due to the nature of the install ?

The service fuse carrier is always marked 100A as the max rating of fuse. The fuse would need to be checked to ascertain if the tails need fusing down after it.

Theres definitely no rcd protecting the tails; my issue is I cannot see if the t&e is mechanically protected or not when it goes into building so will note this on the cert also. Is it usual to run tails in t&e on new builds and put in conduit ?? That's a really subjective question.

Second thoughts its a lash up, t&e comes out switch fuse (also stating 100A) through a bush and ring, theres no gland; hangs in the air with no fixings then goes into the wall. Lash up if you ask me
 
Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
Is this T&E that goes to the C.U. a sub main?
 
Im not entirely sure as all wiring is back entry into CU, proper tails go from main DNO Fuse to meter and then to switch fuse; from the switch fuse its t&e. So I assume yes it goes to CU
So there is a switch fuse protecting a sub-distribution circuit (sub-main) is this fused down to 60A?. The other issue is the method of its installation.
 
So there is a switch fuse protecting a sub-distribution circuit (sub-main) is this fused down to 60A?. The other issue is the method of its installation.

Its not a sub main, its a semi detached house with its own single phase supply. The switch fuse is there as the tails are longer than 3m, the load side of the switch fuse is t&e which I can only assume is going the the CU. The switch fuse has 100a on it
 
If it's a switch fuse the consumer side of the meter then you can remove the fuse to check.
 
If you are saying that the meter tails are 16mm from the switch fuse with hopefully a 60A fuse that is perfectly acceptable as long as certain criteria is met overcurrent is afforded by the 60A fuse so just need to ensure there is short circuit protection.
It is the same principle that you find when switch-fuses are joined onto a bus-bar chamber.
 
I'd say that by virtue of the switch fuse being present the 16mm T&E is a sub-main. I'd just check the fuse in that and fit a 60a cartridge if necessary. And it's only recently that this sub-main requires RCD protection to be compliant [Assuming reasonably low Ze] so in my opinion that doesn't make it dangerous. Just note it on the certificate.
 
I'd say that by virtue of the switch fuse being present the 16mm T&E is a sub-main. I'd just check the fuse in that and fit a 60a cartridge if necessary. And it's only recently that this sub-main requires RCD protection to be compliant [Assuming reasonably low Ze] so in my opinion that doesn't make it dangerous. Just note it on the certificate.

Okay, never considered that would be called a submain so that's good info. Will check tomorrow when the house was constructed but im sure it no older than 5 years.
 
The regulation regarding a cable buried within the wall at a depth equal or less than 50mm being RCD protected has been around from at least 2008 17th edition reg 522.6.6 refers.
 
Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e.
I did nor remove the fuse carrier to check the actual fuse as it was sealed :rolleyes:

Anyhow my point is, ive already installed new circuit and have to issue an EIC, I will be writing in comments box write what I found and that it looks wrong. However looking forward what should I do about this. The customer wont be happy me turning off all the power; I told him to contact the people he bought the house from and raise the point.

Another thing I found includes a spur that don't switch off the load in garage that its labelled to do. Its not right is it, brand new house as well, and theres hundreds of them.

The distributers protection (service head bullit) on a condition report should normally be recorded as a "LIM"...

Next, use your intuition to determine what the max. Demand for each supply is/should likely be...
P.S.
It won't be 80 chuffin amps...thats for sure...


The bigger issue here for me...is whether or not it complies with the requirements of certain DNO's in regards to length of run from the service head (usually 3 meters...i think)...
 
Last edited:
The bigger issue here for me...is whether or not it complies with the requirements of certain DNO's in regards to length of run from the service head (usually 3 meters...i think)...

It's fed from a switch fuse though.
 
Its not a sub main, its a semi detached house with its own single phase supply.

Submain Is the common name for any distribution circuit which is part of the consumers installation. The type of property or incoming supply is irrelevant, if it is a circuit with ocpd etc on the consumers side of the meter and it feeds a DB, CU etc then it is a submain.
 
Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
DSCF2004.JPG
DSCF2005.JPG
DSCF2006.JPG
DSCF2007.JPG
 
Last edited:
Glanding into the switch-fuse could be better. Looking at the photo's I am guessing that the 16mm T&E goes up into the cavity which can have its own non-compliant issues and then in joist space to consumer unit at ceiling height that way removing the requirement for RCD protection. Although in practice the house would not normally take 80A more like 40A and the 16mm can take that the cable should be rated more than the fuse rating. 80A is on the borderline of clipped direct.
 
Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
View attachment 48408 View attachment 48409 View attachment 48410 View attachment 48411

I might of glanded em if it were me...
But I've seen plenty of entry's into enclosures done like that...
The bit where they've appeared to have just brayed a hole in the side of whatever it is looks a bit dog Shyte though...
 
Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
View attachment 48408 View attachment 48409 View attachment 48410 View attachment 48411

I might of glanded em if it were me...
But I've seen plenty of entry's into enclosures done like that...
The bit where they've appeared to have just brayed a hole in the side of whatever it is looks a bit dog Shyte though...
 
A few years ago I took an Nic inspector to an EICR as part of my annual visit. It had 16mm tails but the cutout was an older type with 60a fuse. I had put the tail size was Ok for the fuse although I hadn't checked it physically (it was a 60a cutout). He argued the ---- with me. I said I hadn't removed it as it was sealed but it was a 60a cutout. He wouldn't leave it and made me confirm in writing after a physical inspection by DNO the size of the fuse!
 
Have the rules changed ?? Assess the maximum demand of the installation, if this does not exceed 60 Amps then 16mm tails are acceptable. I think NICEIC inspector told me this. Make a note on the certificate. It's important that any additions to the connected load do not exceed the rating of the tails.
 
Have the rules changed ?? Assess the maximum demand of the installation, if this does not exceed 60 Amps then 16mm tails are acceptable. I think NICEIC inspector told me this. Make a note on the certificate. It's important that any additions to the connected load do not exceed the rating of the tails.
Hibreasoning was that because I hadn't physically inspected the fuse it could be 100a protecting tails rated at say 80a.
 

Reply to 16mm T&E tails on 100amp fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
453
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
936
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock