Discuss 16mm T&E to Consumer Unit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hogey

Afternoon everyone, I've just been to a neighbours house who has just her home completely done up as the foundations are shot. The house has been rewired and in doing so the consumer unit has been moved to one side of the house (the main fuse is outside on the other side of house). I've gone to swap a light fitting over for her and have noticed the elec contractor who's rewired it has used 16mm t&e supply. The cable is buried within the wall so not sure what protection they've used, i might dig out some of the plaster to see. The main fuse is an 80A (the seal has been cut off the fuse carrier so i checked). There are 1 x 10mm for shower, 1 x 10mm for cooker, 1 x 10mm for hob, 3 x ring circuits, 1 x radial and 3 x lighting circuits. The job must have been signed off already and I haven't done any cable calcs yet but it just doesn't sit right with me. Has anyone came across this before? Opinions? Thanks in advance.

Ste
 
How far does the cable run, how is it installed, has it been given circuit protection, where are the main protective bonds connected.
 
It has been rewired within the last 6 months. The cable run must be 15m give or take, bonding comes from the main earth block at meter cupboard, no RCD on the 16mm T&E though (sorry was meant to say that), it's wired into a separate DP iso, i think 100A but will double check.
 
A quick referral to table 4D5, suggests the best ccc for 16mm tw&e is 85a (clipped direct). So with 15m negotiating through the house, can't see how its ever going to suffice? And as it buried in a wall, chances are without earthed steel plate capping, its going to need additional protection

Seen it may a time mind.
 
How is the T&E connected at the origin? Because the way I'm picturing it there will be non-sheathed conductors outside of any enclosure or containment at that point.
 
Hi Guys, sorry haven't had chance to reply... Yes they have taken a separate 16mm earth from main earth block to the C.U. The 16mm T&E goes from a 100A iso just past the meter to the C.U. inside the house, it's not a great job tbh... I'll upload a pic. Point still remains that IMHO 16mm T&E isn't fit for purpose in this instance. I don't really wanna get involved as haven't done any work there and its a ballache to rectify but i guess it's my duty...
 

Reply to 16mm T&E to Consumer Unit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
790
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
838
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
591
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
753

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock