Search the forum,

Discuss 18th Edition Energy Saving Matters in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
I've not read any of the 18th edition drafts but have read some summary points of what to expect. I understand there will be some emphasis on energy conservation. Is anyone aware of what this will entail (in domestic installs) other than low energy lighting?
 
Unsure how true but I have heard there will be emphasis on using increased conductor sizes to minimise heat loss in cables.

I can see us running 10mm ring mains on 20A MCBs! :D

The last few jobs I've run the consultants have specified 2.5mm lighting circuits on 10A MCBs and 4mm ring mains on 32A MCBs. I suspect out of shear laziness. Why do a cable calc when you can just oversize everything?

The job I'm currently running has a 32A supply for a trace heating system, 15 meters in length with a 16mm twin and earth with a separate 16mm 6491B CPC! Crazy!
 
We've only got till July next year to find out.

I'm saving up my pennies, so I can spend it on a lovely course to tell me how to use an index, and answer some questions, currently around £400ish. :mad:
 
Had an niceic assessment today and he said the assessors have been told at a meeting that the energy saving secrion has been reduced alot from the draft.
Likewise the earth rod issue has been delayed. So hopefully nothing too drastic coming in it now.
 
it is bloody drastic. £70 's worth drastic. i for one will not be wasting beer money on it.
 

Reply to 18th Edition Energy Saving Matters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm facing a dilemma and any advice would be hugly appreciated. I'm transitioning from the military into becoming an electrician. I've completed...
Replies
19
Views
3K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
606
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
786
Hey all, I’m an electricians mate, trying to get fully qualified but struggling. I’ve got my L3 diploma (C&G 8202-30) and 18th edition, I have...
Replies
1
Views
2K
Experienced Electrician, C&G 236 Parts 1 & 2, AM 1 & 2 18th Edition Am 2. (JIB Gold Card) I've been out of the trade for some time, but did a...
Replies
2
Views
937

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock