Search the forum,

Discuss 1950s IM Power Relay Timer Help for Solenoid Valves in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
18
Hi there

Complete novice electrical wise. I am refurbishing an old 1950s Injection Moulding machine and looking to replace the Power Timer Relays. So far with no success myself and two attempts. It appears I need some expert help. I would love direction on the type of timer I need and a link to where I could purchase is a bonus. Any help much appreciated. Details below:

The old Timers:
1645685277155.png


What I've investigated:
  • There are 2x Timers, one for inject and one for clamp
  • They are both the same, because I can swap them around and it still runs just fine
  • Markings still remaining on one says Supply 230 V AC and Rating 6A 230 V AC. There is no cut down in power on this machine, 240V throughout.
  • They appear to be short-circuit driven (not power on all the time and Start commands etc)
  • Power is only supplied when they run and is instantly straight through to the output
  • 11 pin circular configuration
  • Phase to pin 2, Neutral to pin 10
  • Power into pin 5 and 2 makes the output run forever until short-circuited. I think I've heard this called an Inhibit function which allows the Timer to pause and force power through pin 6. In the clamp instance this forces the clamp closed, lets the inject sequence run, and then allows the Timer to run before cutting power and releasing the clamp.
  • Pin 6 is the only output. This runs to the 5/2 solenoid valves and changes the valve position for either inject or clamp
  • Timer appears to be a Power Off Delay or similar as it only tells it when to cut power off

Diagrams that I've mapped to help explain how the Timers work and current wiring:
1645685398265.png


1645685420357.png


If you need any more info I'm happy to provide. And even if you are just interested in the machine I can post pictures of that also :)

Thanks
Murdoch
 
Interesting... will take a closer look later. Might be a silly question but if the relays work, why are you replacing them?

I am not sure what you mean by 'short-circuited' as far as the output is concerned. I would read that as a short between line and neutral that would blow the fuse, but clearly you mean something else. Can you please clarify...
 
This sounds like one that might interest Lucien!
Relays and timers, etc that use this style of plug in base are still available today, but to preserve originality, you're probably going to have to carefully open up the faulty one and see what the problem is. If beyond repair, there's plenty of room to fit a modern replacement inside the can an seal it up again'

Edit: I see I was right! Lucien has replied while I was typing this.
 
This sounds like one that might interest Lucien!
Relays and timers, etc that use this style of plug in base are still available today, but to preserve originality, you're probably going to have to carefully open up the faulty one and see what the problem is. If beyond repair, there's plenty of room to fit a modern replacement inside the can an seal it up again'

Edit: I see I was right! Lucien has replied while I was typing this.
Thanks brianmoooore, yes I've seen Lucien has replied so hope they can help :) I've tried two 11pin new timers and failed so getting the right one is the challenge
 
Interesting... will take a closer look later. Might be a silly question but if the relays work, why are you replacing them?

I am not sure what you mean by 'short-circuited' as far as the output is concerned. I would read that as a short between line and neutral that would blow the fuse, but clearly you mean something else. Can you please clarify...
Hi Lucien

Thanks for replying. Yes they do actually still work and I can run the machine through a full sequence. Unfortunately the dials and knobs and internals are all a bit knackered. So each time I come back to the machine it has vibrated and the dials moved around or if I tighten too hard it goes past and spins the case. So in short, repeatability so that when I get molds I can simply set it to 2 for example and it is 2 :)

Sorry I'm not fully up on the electrical lingo (a designer myself). But basically I'm trying to describe that there isn't power to these timers all the time like more modern versions of the 11pin. The modern ones appear to have power all the time and then trigger a start sequence. Where as these old ones appear to just get up and running once the power is applied to either 2 or 2 and 5. Then outside of itself in the sequence it is tripped and power disconnected. Does that make sense?

The two timers I have tried and failed with are:
H3CR-A (knock off version of this link below)

TR-6162U

Here's a look inside the cabinet:
1645745394264.png


And machine if of interest:
1645745455553.png
 
Could you tell us what is stamped on the plate circled A? See attachment.

Circled at B are the connections to pins of a device; which one? Could you show these too if they refer to the relay you wish to source new?
 

Attachments

  • timerrelaysnz.jpg
    1.8 MB · Views: 16
Could you tell us what is stamped on the plate circled A? See attachment.

Circled at B are the connections to pins of a device; which one? Could you show these too if they refer to the relay you wish to source new?
Hi Marconi

Sure, here is a close up of the stamp and my guesses:

Type: ET P1 TIME
Ref: R1783 0.2-5 SECS
Supply: 230 V50 AC
Rating: 6A 230 V AC

1645832683406.png


And as for some new ones I'm wondering about there are these:

Macromatic Analag Timer TAA2U
1645833130839.png


Autonics AT11EN
1645833303333.png


From my understanding the numbers 3, 4, 8, 9 are internal to the Timer. But where I struggle is, what is considered an Output and Input. Because from the looks I require Input to 5 to inhibit. And then I want 6 as the Output to the solenoid valve. I also see the - and + are the other way around on these timers.

Any help appreciated :)
 
I
Hi Marconi

Sure, here is a close up of the stamp and my guesses:

Type: ET P1 TIME
Ref: R1783 0.2-5 SECS
Supply: 230 V50 AC
Rating: 6A 230 V AC

View attachment 95470

And as for some new ones I'm wondering about there are these:

Macromatic Analag Timer TAA2U
View attachment 95471

Autonics AT11EN
View attachment 95472

From my understanding the numbers 3, 4, 8, 9 are internal to the Timer. But where I struggle is, what is considered an Output and Input. Because from the looks I require Input to 5 to inhibit. And then I want 6 as the Output to the solenoid valve. I also see the - and + are the other way around on these timers.

Any help appreciated :)
I will study these over the weekend. I have found this firm which does a wide range of 11 pin timers both electronic and mechanical. There are others of course. Just need to determine the functionality and pin out to select the correct replacements:

Foxtam Electronic Timers - Foxtam Controls - https://www.foxtamcontrols.co.uk/products/foxtam-electronic-timers?gclid=CjwKCAiAvOeQBhBkEiwAxutUVHSvHPRKJ82h19_XRP_x6cjnG9xgrFnutB03_ZHWCQ_b9qyrUHY_OhoCuRoQAvD_BwE
 
mud_the _nerd: Do you have a multimeter with an 'Ohms' range? If not could you buy a cheap digital one?

If you look at the attachment you will see two identical tables. The numbers refer to the pins on the relay. Using a multimeter please measure first the resistance between pin 1 and then to each of pins 2 to 11 of the black round timer and enter the meter reading in the table. Then do the same for pin 2 but this time to pin 1 and the each of 3 to 11. Then pin 3 but to 1 then 2 and then each of 4 to11, etcetera.

The first table is for when the timer is set to zero seconds. The second table for when it is set to say 5 seconds.

The resistance between the pins will be a low value apart from I think between pins 2 and 10.

I hope this is clear. Then return the two tables to me as an attachment.
 

Attachments

  • Connection Matrix.docx
    12.2 KB · Views: 11
Chances are that there is a modern version of what you want available, but it will likely be more sophisticated than the original, with unwanted additional functions built in. These you may have to disable, or ensure that they are not accidentally enabled.
 
Further to my last post; could you remove the black T1 and the white timer T2 and the heat relay and then take a photo of the wiring to their bases? Also take a clear picture of the terminal block so I can see which wire goes in to which terminal and to where the other ends go on the three relay bases.

Or you could do the wire tracing for me and send me a diagram. Do you have the manual for the machine with its wiring diagram inside?
 
Further to my last post; could you remove the black T1 and the white timer T2 and the heat relay and then take a photo of the wiring to their bases? Also take a clear picture of the terminal block so I can see which wire goes in to which terminal and to where the other ends go on the three relay bases.

Or you could do the wire tracing for me and send me a diagram. Do you have the manual for the machine with its wiring diagram inside?
Thanks so much for looking into this. I don't have a multimeter but I think I will buy one so I can test for you.

I actually stumbled on this article which might shed some light. It looks like timers that old might have been True Off Delay timers rather than more modern Off Delay timers. https://www.macromatic.com/blog/relays/what-is-a-true-off-delay-function

"Upon application of input voltage, the output is energized. When the input voltage is removed, the time delay (t) begins. At the end of the time delay (t), the output is de-energized. Input voltage must be applied for a minimum of 0.1 seconds to assure proper operation. Any application of the input voltage during the time delay (t) will reset the time delay. No external trigger is required."

From a search I can find some 240v 8pin ones of these. But I haven't found a 240v 11pin version. Do you know how I would test to see if a True Off Delay or not?

I do have my own attempt at a wiring diagram. I can confirm the numbers the timers are using as I took off the timers to record where the wires went:
1646001134708.png


Please keep in mind it is only the black large old timers that work. But I found some old pictures I have of inside the cabinet:
1646001368530.png


1646001409644.png
 
I have asked FOXTAM for a quote to supply two 11 pin true delay off timers from this range:

https://www.foxtamcontrols.co.uk/assets/img/25-YRKF-8RKF-11RKF-8R2KF-11R2KF.pdf

The timer above does not require a 230V ac power supply to be present to maintain the contacts closed during the delay off period.

I will also look at other suppliers such as RS components.

I will explain later how you can use three lamps connected to the terminal strip to confirm the functionality of the timers. You do not now need to fill in the connection matrices I mentioned earlier.
 
Last edited:
murd_the_nerd:

Please remove the wires marked with a short blue dash in the attachment called 'disconnection'. Label them so you know were to connect them back to. Put the ends of these wires inside a connector so they do not touch anything. This will disconnect the valves and the heater.

Buy three neon lamps like these:

IND5032405-240-T/RD | CAMDENBOSS Red Indicator, 240V, 8mm Mounting Hole Size, Lead Wires Termination | RS Components - https://uk.rs-online.com/web/p/indicators/0576181?cm_mmc=UK-PLA-DS3A-_-google-_-CSS_UK_EN_Displays_%26_Optoelectronics_Whoop-_-Indicators_Whoop-_-576181&matchtype=&aud-832474874771:pla-302376642891&gclid=CjwKCAiAgvKQBhBbEiwAaPQw3PKQPeh7zExzTVve1WMoT2jRpbFI38x3yiulbOparbQKTL-P_mZxfxoC1tgQAvD_BwE&gclsrc=aw.ds

They are 230V ac neon indicators pre-wired with leads. Amazon will do them.

Labels these indicators as L1, L2 and L3. Now connect these lamps as I show in the second attachment 'ThreeLamps'. The leads go to the terminals at which you had disconnected a wire and the neutral.

You can now run the control panel and the lights will indicate power being supplied to the two valves or heater so that we can confirm the functionality of T1 and T2 as True Timed Delay off.
 

Attachments

  • threelamps.jpg
    1.2 MB · Views: 17
  • disconnections.jpg
    1,007.5 KB · Views: 16
murd_the_nerd:

Please remove the wires marked with a short blue dash in the attachment called 'disconnection'. Label them so you know were to connect them back to. Put the ends of these wires inside a connector so they do not touch anything. This will disconnect the valves and the heater.

Buy three neon lamps like these:

IND5032405-240-T/RD | CAMDENBOSS Red Indicator, 240V, 8mm Mounting Hole Size, Lead Wires Termination | RS Components - https://uk.rs-online.com/web/p/indicators/0576181?cm_mmc=UK-PLA-DS3A-_-google-_-CSS_UK_EN_Displays_%26_Optoelectronics_Whoop-_-Indicators_Whoop-_-576181&matchtype=&aud-832474874771:pla-302376642891&gclid=CjwKCAiAgvKQBhBbEiwAaPQw3PKQPeh7zExzTVve1WMoT2jRpbFI38x3yiulbOparbQKTL-P_mZxfxoC1tgQAvD_BwE&gclsrc=aw.ds

They are 230V ac neon indicators pre-wired with leads. Amazon will do them.

Labels these indicators as L1, L2 and L3. Now connect these lamps as I show in the second attachment 'ThreeLamps'. The leads go to the terminals at which you had disconnected a wire and the neutral.

You can now run the control panel and the lights will indicate power being supplied to the two valves or heater so that we can confirm the functionality of T1 and T2 as True Timed Delay off.

Thank you so much for the idea of testing with light bulbs and the link to a timer. I think only after testing can I confirm whether it is a True Off Delay or something different. There are a few other types that allow timing on power input such as Interval or Watchdog. Some with a trigger and some just with input:
1646095378061.png


And watchdog:
1646095406918.png


Because the machine does completely run and the sequence relies on other sensors such as clamp close. I think I'm best to skip the lightbulbs and use a multimeter. I have just ordered one. Can you please confirm if this test method will work:

Step 1
Plug multimeter common in. Then test input 2 and input 5 (one by one) while timer is off. There should be no power to either.

Step 2
Let the sequence run so the clamp is closed. This somehow uses input 5 to initiate, either a once off trigger or continuous. Plug multimeter into 2 and 5 (one by one) to see if there is continuous power or not during this state in both. My assumption is that there is continuous power to both.

Step 3
Let the sequence run past inject to clamp open. This is when the clamp Timer is actually using the timer delay. Plug the multimeter into 2 and 5 (one by one) to see if there is continuous power or not. I assume there isn't to 5 or the Timer wouldn't run in delay mode. And if there is power to 2 then it isn't a True Off Delay. Lastly, if there is no power to 2 then a True Off Delay timer is exactly the one!

With testing input 5 I will also be able to confirm whether it is a quick burst of power or continuous. I assume it is 240v which means if continuous I need a Power Trigger version of the timer as it will blow otherwise.

How does that sound? Thanks so much for clearing up a great testing approach for this :) Looks like I'm going to learn how to use a multimeter!
 
At the moment I am trying to simply replace the timers T1 and T2 with 11 pin equivalents and at worst only have to rejig the wiring to the 11 pin sockets. I will phone FOXTAM today and another company which sells their products.

If I cannot find an 11 pin true time delay off, then what we may have to do is use a more common delay off timer which requires a permanent power supply straight from the power input line and neutral and a trigger input derived from the supply to terminal 2.

As you say, it is clearly important to know the required timer functionality hence the care we are taking to establish that.

Please wear some rubber gloves such as washing up gloves and some eye protection when you use the multimeter on the live equipment and make sure it is set to the highest ac voltage and the leads go into the volts terminals on the meter. Some meters have a third terminal for measuring current.

As well as measuring between 2 and 5 to see if the timer is energised, also measure between 5 and 6 to see when there is a voltage to the valves. These numbers refer to the relay socket terminals. Please draw a timing diagram like the ones you have shown.
 
Last edited:
At the moment I am trying to simply replace the timers T1 and T2 with 11 pin equivalents and at worst only have to rejig the wiring to the 11 pin sockets. I will phone FOXTAM today and another company which sells their products.

If I cannot find an 11 pin true time delay off, then what we may have to do is use a more common delay off timer which requires a permanent power supply straight from the power input line and neutral and a trigger input derived from the supply to terminal 2.

As you say, it is clearly important to know the required timer functionality hence the care we are taking to establish that.

Please wear some rubber gloves such as washing up gloves and some eye protection when you use the multimeter on the live equipment and make sure it is set to the highest ac voltage and the leads go into the volts terminals on the meter. Some meters have a third terminal for measuring current.

As well as measuring between 2 and 5 to see if the timer is energised, also measure between 5 and 6 to see when there is a voltage to the valves. These numbers refer to the relay socket terminals. Please draw a timing diagram like the ones you have shown.
I love the approach and a straight 11pin replacement would be amazing!

I'll let you know once my multimeter has arrived and I've had a chance to run the machine. Then I can playback what terminals are live when in the timing sequence. This will hopefully give us enough info to determine the Timer type. Happy to draw a diagram with terminal numbers and live status.

This may be 1-2 weeks as deliveries are scrappy here right now due to the pandemic...
 
Please draw a timing diagram like the ones you have shown.

Hi Marconi

My new multimeter arrived and I have had a chance to check voltage in various states. I think this has given us valuable insights and I've added detailed diagrams below. Any help much appreciated :)
  • Looks like we're dealing with a "power trigger" as I could see 230V continuously being supplied to T-5
  • There appears to be an interruption where I've marked in yellow. Its like the first time it is powered up it runs continuously and then after interruption it then carries on with the time delay. I'm kind of assuming this interruption is on T-5 or both T-5 & T-2 but not sure.
  • Interestingly on Manual Mode Inject the output is energised with just input to T-5
  • In Auto Mode both timers start with power supplied to T-2 & T-5
  • Interestingly on the Inject Timer, even though the output is de-energised after time delay is finished, power remains on the inputs until reset by the system.

1647214067513.png


1647214087717.png


1647214113550.png
 
murd-the-nerd: I am finding it difficult to follow your wiring diagrams, particularly at the various switches and timer bases. Your recent power versus time diagrams help but I do not have sufficient information even with them to be confident about naming a suitable substitute for T1 and T2. The best I can say confidently is that for T1 and T2 the connections at the top of the base connect to what we call 'volt-free' contacts but these may be either NC or NO - I reckon they are NO.

Do you want to send me the timer(s) you wish to replace to study? You did say T1 and T2 are the same so why not send me just the black Kiwi one?

Regards

Marconi
 
Or you could connect those neon lamps I mentioned. Connect a neon across the 2 and 10 terminals to indicated when the relay is energised. Also connect a neon between relay output T6 and neutral to indicate when their relay contacts are closed/open. Finally a neon between T5;and neutral. Then label up the lamps and film the sequence. Post as an attachment For me to look at.
 
Hi Marconi

Sorry for the delay in my response. Seriously you have been a big help thank you! I am all the way in New Zealand so I think postage not really an option but thanks for the offer. To be honest I think we are really close. Yes T1 and T2 are the same, I have swapped and it still functions just fine.

I have tried to add switches to the diagram and fleshed out how important the Sensor is to the sequence. I haven't had a chance to use the Multimeter and validate this. But in practice (from me using the machine) this is how it works. I've colour coded the T1 and T2 so you can see the exact pin number that goes to the solenoid valves. This is becoming clearer each time I iterate :)

Heating ON and Auto Mode ON
To begin Auto sequence press Button LEFT & RIGHT at the same time. While held power is directed to T1 CLAMP and the Clamp Valve. Once the Sensor CLAMP is engaged you can depress the Buttons. Power is now directed to both T1 CLAMP and T2 INJECT via the Sensor. Once the timer runs out on T2 INJECT the Inject Valve is released. Once the timer runs out on T1 CLAMP the Clamp Valve is released. This trips the Sensor CLAMP and power is removed from both T1 CLAMP and T2 INJECT. The sequence is reset.

1647741473223.png


It actually seems that if I am happy to remove MANUAL mode a simple INTERVAL timer with the same pin config would work just fine:
1647741995601.png


At this stage what is confusing me the most is where the heck is the OUTPUT on these diagrams? This is an example of a power trigger but I see nothing out of pin 6... though in the non-power trigger version there appears to be... Maybe we are after a simple trigger version that allows voltage input to trigger?
1647742267102.png


Ohh and I am happy to open up the Timers and take pictures, but I'm not sure we'll learn anymore than what I have diagnosed with the multimeter.

I hope the new diagram makes better sense! :)
 

Attachments

  • 1647742138628.png
    40.1 KB · Views: 7
First response today. The switch outputs for the TR relays are the two sets of contacts 1, 4, 3 and 8,9, 11.

For the equipment’s relays T1 and T2 the switch output is 5,6 (and maybe 7).

The triggering for T1 and T2 is caused by the application of mains power across 2 and 10. When this happens the timer function of T1/T2 starts and results in the closing of the T1/T2 internal contacts connected between their 5 and 6 terminals. By applying mains Line to terminal 5 a device can be switched according to the timer function by connecting it to 6 and Neutral.

In summary for now 5, 6 on T1/T2 are not trigger inputs as they are for the TR series of relays you show function and terminal diagrams for.

If the timer function of T1/T2 is triggered by power applied to 2 and 10, then we could use one of the TR series and rejig the wiring to its base so that it performs just like a T2/T2. The switching - what you mean by output would done using one triplet 1, 4, 3 or 8, 9, 11 with a Line being connected to 3 or 11 and the load to 3 or 9 respectively.

What remains to be clarified is the timer function actually required so that the TR operates like the T1/T2. This is what we need to know next. I suggest the use of the neon lamps so the timer function can we watched. My earlier post refers.

Note well- as the panel is currently wired you cannot use any of the TR relays because your panel uses 5 and 6 as contacts to switch mains power whereas the TR relays uses them as input start timer function triggers.

🙂
 
Ahh so it appears the wiring on these is super weird having the relay output on 6! So far I haven't seen a single timer that has that. They always appear as gate, start, reset type functions. And from your notes above does that mean I wire the relay output (solenoid valve in my case) to 3 or 9 as highlighted below on a few timer variations. This timer does appear to accept power to 5 as well. Link here:

1647827729202.png


If you confirm above then I might finally understand these diagrams :)
 
Small typo corrected in:

'Note well- as the panel is currently wired you cannot use any of the TR relays because your panel uses 5 and 6 as contacts to switch mains power whereas the T1/T2 relays uses them as input start timer function triggers'.
 
Ahh so it appears the wiring on these is super weird having the relay output on 6! So far I haven't seen a single timer that has that. They always appear as gate, start, reset type functions. And from your notes above does that mean I wire the relay output (solenoid valve in my case) to 3 or 9 as highlighted below on a few timer variations. This timer does appear to accept power to 5 as well. Link here:

View attachment 96189

If you confirm above then I might finally understand these diagrams :)
Yes - on the 11 pin there is a set of NO contacts between terminal 1 and the circled in yellow terminals which could be used to control power to the clamp and solenoid. Your application relies on power being applied to 2 and 10 to start the timing function which determines how/when these contacts close and open. As I said we can rewire the base to use these NO contacts.

Finding a suitable replacement relay is not the current main effort - that can be done easily. What we need to confirm is what timer function is required when power is applied to 2 and 10. eg: Interval, delay on........
 
Great, then I think we've done it pretty much!

Changes would be:
  1. Change wiring as per 'After' diagram below if sticking with an 11pin timer
  2. Use a timer that starts with power input to 2 and 10
  3. Use an Interval type timer as my system continues power to input 2 past the timer ending (Interval was the only type I could see that lined up with this). I've updated the chart to represent what I'm seeing with the multimeter and ignoring 5. The flicker I eluded to before is likely the change from button power input to clamp sensor power input. And this is likely to not influence the timer as power still continuously supplied.
  4. Don't mess with any gate or start inputs. You can see in the T1 Clamp wiring it is simply folding over power to both 5 and 2 at the same time. So there really is no need for it and all the modern timers I've found need a signal input, not continuous power to 5.
From my research this is actually far more common on 8pin timers. And they are about half the price. So there could be an argument to change the 11pin to an 8pin.

1647906817022.png


1647906850506.png


1647906883654.png


Example timing chart for Interval on an 8 pin:
1647907283544.png
 
Your after wiring diagram needs a wire from the relay base 11 to the connector block 4 as shown in my attachment.

If you buy a couple of power (230V ac) initiated interval timers you can replace T1 and T2. If you are not sure send me a link to the ones you intend to buy and I will check they are suitable. Obviously they need to have suitable interval time range. The contacts only carry the small current to operate clamp and inject actuators. Up to you whether to go for 8 pin, 11 pin or din rail ones. Happy to check a photo before you power on should you want me to.

Please keep me informed on progress and DO NOT WORK on live equipment.

🙂
note: For power initiated interval timer if applied power goes off then interval output ends at same time.
 

Attachments

  • 1647906850506.png
    246 KB · Views: 13
Brilliant! I thought the timer power actually supplied the output power. How silly of me. But according to your diagram each Relay in the Timer can have its own power and the Timer simply switches the NC & NO contacts. So you could actually have a set up like this and mix voltages and all sorts:
1648005880389.png


This has helped me greatly as I completely missed I need to supply power to the contacts! Thanks so much :)

I will get on to ordering some Interval Timers that function with Power ON and report back how it goes
 
And I'm thinking of going for something like this. The 8pins really are more geared to the Power On Interval style and the 11pin options are less common and expensive! The 8pin option below looks like it will do the job just fine :) One caution might be the 3A vs 6A on current Timers, is that something I should worry about? It is just supplying voltage to a solenoid valve, I can't imagine it drawing a huge amount of power.

Be thankful you don't live the next stop to Antarctica, things are hard to come by down here! The 8pin timer is in stock in Australia so quicker postage. I can get unbranded ones for $10-15 from aliexpress but figure I should get the real deal to be safe and postage can be up to a month.

AT8N
NZD$58

Spec sheet:
1648017648588.png

1648017672723.png



And the much more expensive 11pin option (and I'm sure others too):

TD-78121
NZD$216

1648018058699.png

1648018272977.png


Great to be at this stage of the process and purchasing new Timers :)
 
The relay you have selected is suitable. Order AT8N . (Do not order AT8N1 or AT8N2 ).

One they have arrived we need to set up the timer range and timer mode for I = Interval operation.

You will require two 8 pin bases.

Study the connection diagram carefully for the AT8N so that you place the wires correctly to the 8 pin base.

The current switching capacity of this timer relay is satisfactory for your loads.

Also check by inspection and then with your meter on low ohms range that all items of the machine which are made of metal are indeed connected together and to the earth pin of the plug.
 
Nice one and good memory! I have received the new timers and bases. But unfortunately the family household I have my machine stored at came down with Covid so I haven't had a chance to do the wiring and install yet. Hoping to get over there in the next few weeks. Will keep you posted :)
 
Hi Marconi. I finally had a chance to wire in the new timers today :) I was in a bit of a rush and may have got the + & - the wrong way around. The heater wouldn't start so there is an issue. I either need to force the sequence change on the machine or the wiring is not letting it turn on. There is a relay in series with the two timers (- black wires) that allows the heater to start. I ran out of time to trouble fix.

I would appreciate if you could let me know whether switching the + & - between timer pins 2 and 7 would change anything? It seems just for DC it is wired the other way. Everything else appears fine at first glance...

New wiring:
1651037512441.png


New vs Old timers:
1651037599415.png


Timers and relay wiring new vs old:
1651037649869.png


Wiring diagram from the timer manual:
1651037695550.png
 
Just a quick question - did you select the correct timer operation mode - interval on or mode I?
 
Last edited:
With power off and referring to any pictures of the relay wiring before you swapped for new ones just check you have moved the red wires to the new bases so they act as relay power or output contacts as necessary.

What do the top left and right lights do?
 
Hi Marconi. I finally had a chance to wire in the new timers today :) I was in a bit of a rush and may have got the + & - the wrong way around. The heater wouldn't start so there is an issue. I either need to force the sequence change on the machine or the wiring is not letting it turn on. There is a relay in series with the two timers (- black wires) that allows the heater to start. I ran out of time to trouble fix.

I would appreciate if you could let me know whether switching the + & - between timer pins 2 and 7 would change anything? It seems just for DC it is wired the other way. Everything else appears fine at first glance...

New wiring:
View attachment 97046

New vs Old timers:
View attachment 97047

Timers and relay wiring new vs old:
View attachment 97048

Wiring diagram from the timer manual:
View attachment 97049
It is only for dc supply you need to connect plus and minus as in the wiring diagram.
 
Thanks for confirming the +/- only being an issue for DC. No lights or anything on the timers because without the heater relay working the sequence won't even start. And power is only supplied at the time.

Hmm maybe a stuck sensor or something not to do with the timers at all. I will investigate in the coming weeks and hopefully have some good news!
 
@marconi we have victory!

1651641123965.png


Turns out the new wiring of the timers was perfect. And the issue was with the heater relay itself. I found a loose wire, fixed that and then all worked perfectly. I don't think I can post a video on here so I've just snapshotted a picture here with the Clamp timer running and output live in interval mode. I can now see the indicator lights on and off during the sequence which is an added bonus with the new timers.

1651641079185.png


Thank you soo much for your help. I wouldn't have made it without you! How lucky this forum is (and me) to have you offer your expertise to problems like this 👍
 
Thank you for the update and nice comment. Would you mind taking a video using your phone and then converting it to MP4 format - there are free converters on-line - and then attach it as a file - see below - for us to see the machine in action please.

Remember there is also the check of earthing and state of cabling to be done and any other mechanical aspects to confirm as safe.
 

Reply to 1950s IM Power Relay Timer Help for Solenoid Valves in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
609
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
872
I am trying to replace a mechanical switch from an OLD ice machine with an electronic timer. The existing switch has only 3 wires, a Black Power...
Replies
1
Views
2K
As the title suggests I'm short of power source options to take the power to the plate with 3 way switch (4 in the US). I've seen on youTube that...
Replies
3
Views
3K
Background I live in Indonesia, the voltage for residential buildings ranges from 220 V to 230 V, I need help with the installation of the...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock