Discuss 2 electric showers and melted live wire from relay in the UK Electrical Forum area at ElectriciansForums.net

Jberry

-
Reaction score
1
This unit is running two showers. Unit was smoking while one shower was running, never tripped the safety switch. Power to one shower is cut off while the other is in use. Is it ok just to change out the relay that had burned? I'm not an electrician but one will be doing the work. The house is rented and the landlord will be arranging the repairs but I'm afraid he probably wont send someone who's registered

20190407_214550.jpg


20190410_224157.jpg
 
If you haven't tinkered with the unit, then this has happened before because one of the neutrals appears to have been moved (No. 3 on the burnt contactor is also burned).

If it's a sample of the work the electricians your landlord uses (some of the cabling will be factory fitted as I believe this is an off the shelf unit - it's not that cabling to which I'm referring) then you are justified in your concerns as I can see several non-compliances.
 
Looks like the whole shower circuits need to be looked at, as the neutrals near the burned relay are also damaged.
As @SparkyChick has pointed out, terminal 3 has also received damage previously.

upload_2019-4-10_23-47-38.png


What power ratings are your showers?
 
... Unit was smoking while one shower was running ... Is it ok just to change out the relay that had burned?
Hi JB and welcome. There has been heat damage and I'm not sure if this was due to the cables not making proper connection or whether the contactor has been overloaded. The failure cause should be established and corrected or it will likely just happen again. And the heat damaged cables should be replaced of course.
 
If you haven't tinkered with the unit, then this has happened before because one of the neutrals appears to have been moved (No. 3 on the burnt contactor is also burned).

If it's a sample of the work the electricians your landlord uses (some of the cabling will be factory fitted as I believe this is an off the shelf unit - it's not that cabling to which I'm referring) then you are justified in your concerns as I can see several non-compliances.


Thanks for the reply. No has never been touched by anyone, we have lived here for 5yrs. Landlord has a history of paying monkeys peanuts! He has contacted me tonight to say he is sending round a non electrician to fix, I have assured him he is not!
 
Hi JB and welcome. There has been heat damage and I'm not sure if this was due to the cables not making proper connection or whether the contactor has been overloaded. The failure cause should be established and corrected or it will likely just happen again. And the heat damaged cables should be replaced of course.


Thank you for the reply. I have notified the landlord Sunday gone and I'm still back and forth about having a professional diagnose and fix the problem. He's all about saving Penny's though
 
Looks like the whole shower circuits need to be looked at, as the neutrals near the burned relay are also damaged.
As @SparkyChick has pointed out, terminal 3 has also received damage previously.

View attachment 48760

What power ratings are your showers?


Yes I agree, there are a few wires that appear to be heat damaged. Also terminal 1 & 3 have heat damage also. When we noticed the smoke and strong smell of burning in the kitchen we had to cut power to the unit.

Should the safety cutout switch have tripped before hand? It never did!
 
Don't take any chances at all !
Anything that looks like it is damaged at all
Should be replaced, no if's or but's
Saving a few dollars now,will seem trivial if it burns down later on.

If this is an on going problem ?
Then you need to find out why !
 
The whole thing is totally wrong..
Singles coming in at the top left.
Both showers on protected by just the 1 40amp MCB & RCD?
Do you have a photo of the whole enclosure?
Be a good 1 for the wall of shame
 

Reply to 2 electric showers and melted live wire from relay in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
204
Hi, thanks in advance for any advice here please on a safety worry... My son lives in a rented house and recently got a strong electric shock...
Replies
3
Views
2K
Hello, I have just posted in the Electrician's section one photo and two videos of what I believe to be a dangerous situation of short circuits...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock