Looks like the whole shower circuits need to be looked at, as the neutrals near the burned relay are also damaged.
As @SparkyChick has pointed out, terminal 3 has also received damage previously.
8.5kw & 9kw
View attachment 48760
What power ratings are your showers?
Don't take any chances at all !
Anything that looks like it is damaged at all
Should be replaced, no if's or but's
Saving a few dollars now,will seem trivial if it burns down later on.
If this is an on going problem ?
Then you need to find out why !
Both showers on protected by just the 1 40amp MCB & RCD?
How do you know that?Why not? The contactor setup is there to ensure only one shower is used at any one time.
This type of ‘shower’ contractor board is generally used abroad if I’m not mistaken ?
In 20+ years of doing odd domestic wiring , I think I have only ever come across one of these once and iirc it was made in Ireland
Either way , it looks like a dogs dinner ...
Do you have any electrical safety certificates for the rented property as those would make interesting reading
This type of ‘shower’ contractor board is generally used abroad if I’m not mistaken ?
In 20+ years of doing odd domestic wiring , I think I have only ever come across one of these once and iirc it was made in Ireland
Either way , it looks like a dogs dinner ...
Do you have any electrical safety certificates for the rented property as those would make interesting reading
Dogs Dinner is putting it nicely Dusty, Lash up is a more apt description, a Bert job from down the local if I'm not mistaken.This type of ‘shower’ contractor board is generally used abroad if I’m not mistaken ?
In 20+ years of doing odd domestic wiring , I think I have only ever come across one of these once and iirc it was made in Ireland
Either way , it looks like a dogs dinner ...
Do you have any electrical safety certificates for the rented property as those would make interesting reading