Came across this recently, haven't seen it before. External meter cupboard serving a ground floor maisonette. Early 1960s I'd say (there was no CPC on the lighting circuit, which was wired in PVC pirelli sheathed singles).

I'm guessing that at some point in the distant past the supply was due to be replaced, and the new and old supplies were joined for continuity of supply at switchover. Non contact volt stick suggests both fuses are still live, but obviously take that with a pinch of salt. Can anyone shed any light?

P6031429.JPG
 
Interesting

I don’t think I have ever seen a spur off 1 cut out (presuming the original cutout) to feed another cut out like that before

nice find
 
Very interesting. If both are live it gets a bit interesting regarding fault protection.
It couldn’t be that one of them is a lower fuse and outgoing to somewhere else, surely?!

I’m still trying to work out earthing and what’s going with the henleys on the left.
A good photo, hours of pondering material!
 
Could top one just have links in, and this is a very wacky and strange way to do a looped supply?
Maybe something unmetered like a row of lamp posts or bus shelter?
 
Agree that one surely must be outgoing. There's no reason on a domestic supply to do anything special to avoid interruption during a changeover.

Non contact volt stick suggests both fuses are still live, but obviously take that with a pinch of salt.
No reason to pinch any salt. If your Voltstick is working properly and you know how to use it, they are a reliable and useful tool. The reason people say they are inherently unreliable is that they don't understand how they work and what they detect, therefore misinterpret the indications.

If both carriers contain a fuse then they will both be live because they are connected together. You can discover the configuration by clamping the cable and changing the load on the local meter. If the current in the link cable changes by the same amount, the top one is the supply,. If it doesn't change, the bottom one is the supply, If it changes by a fraction of the load change in a repeatable way, both are energised supplies.
 
I would say that these were Local Authority built and the (reverse fed) cut out on the left is an unmetered but assessed supply to external lighting, posts or on walls on walkways.

Looks like the single green, lower left goes down to the sheath on the lower incoming supply cable.

Additional info which may or may not be usefull.
A friend recently bought a ground floor maisonette.
Outside there is a larger external meter box with 2 cutouts and 2 meters, 1 up 1 down.

The supply from meter to upstairs originally went though into the lower Maisonette then up a service void to above.
This has been cut off and an SWA runs up the outside.

The gas was the same, upstairs ran into the lower then up.
This now has a pipe up the outside.

This is one of 8 and has external lighting fed via a meter in another external box, all 8 split the bill between them.
These were privately built in the 70's.
 
Agree that one surely must be outgoing. There's no reason on a domestic supply to do anything special to avoid interruption during a changeover.


No reason to pinch any salt. If your Voltstick is working properly and you know how to use it, they are a reliable and useful tool. The reason people say they are inherently unreliable is that they don't understand how they work and what they detect, therefore misinterpret the indications.

If both carriers contain a fuse then they will both be live because they are connected together. You can discover the configuration by clamping the cable and changing the load on the local meter. If the current in the link cable changes by the same amount, the top one is the supply,. If it doesn't change, the bottom one is the supply, If it changes by a fraction of the load change in a repeatable way, both are energised supplies.
Agree about the voltstick, an electricians best friend tbh

First item in my armoury for troubleshooting and checking for live/dead especially at sealed cabinets


I keep 2 in my back pocket
 
Thanks for the replies. I hadn't entertained the idea that i was looking at 'one in, one out', but of course that would make sense. I have to go back there briefly on Thursday, so will have a closer look, and try to work out the configuration as per @Lucien Nunes 's instructions.

No reason to pinch any salt. If your Voltstick is working properly and you know how to use it, they are a reliable and useful tool. The reason people say they are inherently unreliable is that they don't understand how they work and what they detect, therefore misinterpret the indications.

This was me, until a very short while ago. Have just been reading up on them here:

Very useful indeed. Particularly when you lift floorboards and you're faced with a dozen cables, and you need to identify which one belongs to a particular circuit.
 
Thanks for the replies. I hadn't entertained the idea that i was looking at 'one in, one out', but of course that would make sense. I have to go back there briefly on Thursday, so will have a closer look, and try to work out the configuration as per @Lucien Nunes 's instructions.



This was me, until a very short while ago. Have just been reading up on them here:

Very useful indeed. Particularly when you lift floorboards and you're faced with a dozen cables, and you need to identify which one belongs to a particular circuit.
Also you can't 'prove' dead with a voltstick

But at the same time proving dead with a 2-wire tester assumes there is actually a reference(N/E) for the 2-wire voltage tester
 
Last edited:
An important point that many people miss. A Voltstick can reliably indicate that something is live even when the best available reference for a 2-lead tester is not trustworthy.
 

Reply to 2 heads are better than 1? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock