Hi, thanks for any advice.
I’ve got a local farmer who has single phase to the farmhouse and 3 phase to the farm and dairy etc. The problem he’s got is when he turns the milking parlour on the house RCD trips. I am a bit stumped as to why and how to remedy. I was thinking when he switches the large load on it must be something to do with that. I can’t see any borrowed neutrals etc between the 2 independent supplies anywhere. Just wondered if anybody out there had any ideas. Many Thanks
 
is the single phase a separate supply or is it 1 phase supplied from the 3 phase?
 
Hi, thanks for any advice.
I’ve got a local farmer who has single phase to the farmhouse and 3 phase to the farm and dairy etc. The problem he’s got is when he turns the milking parlour on the house RCD trips. I am a bit stumped as to why and how to remedy. I was thinking when he switches the large load on it must be something to do with that. I can’t see any borrowed neutrals etc between the 2 independent supplies anywhere. Just wondered if anybody out there had any ideas. Many Thanks
Is the SP Supplied from the TP and N SUPPLY?????
 
I've been caught out by a farmhouse supply being abandoned at some stage and a new sub-main feeding it from a different building. So verifying it is two supplies is first step.
Also interesting to know earthing arrangements at each.
 
Is it actually 3ph or is it split 2ph? The latter is common on farms. Either way, my guess is that it might well be some kind of weird volt drop/surge issue caused by the dairy firing up. I’m rural, very rural Somerset and theres a noticeable drop in energy (lights dim etc) at milking time!
 
It’s 2 separate supplies. The farm used to be all single phase, however the farmhouse ( overhead) was left on original supply and a new 3 phase supply was installed for farm (underground supply). I think they’re fed from same transformer. Thanks
 
When did the fault start, was it immediately after the 3ph supply was installed or has other work been done since?

If none of the above then the fault is probably a bad connection on the main Neutral at the source where both supplies originate, the transformer, if that's the point the 2 separate.
I was thinking along the lines of neutral distortion / harmonics etc myself. You can find some really noisy pumps and compressors in farm stuff!
 
Always start by doing a global IR on the house to see if it could be N-E leakage.

The other thing to remember is RCD trip on current imbalance. Usually the capacitance L-E only leads to a couple of mA of current due to the dV/dt of a 50Hz sine wave. It is possible that a big drop in L volts when the machine kicks in is causing a much higher dV/dt so just enough current to trip the RCD.

So for that do the usual due diligence of ramp-testing the RCD to verify it is tripping normally (no load(s)) and then use a current clamp meter with mA resolution to get an idea if the existing arrangement is a mA or two, or close to 10-15mA from lost of capacitance (usually mains filters on fancy electronics).
 
Thanks for all the advice. I’m going back Monday so will report back as soon as I’ve done IR tests etc. I also have a power quality analyser so might put that on it for a week as well.
 

Reply to 2 supplies to property and the one trips the other out!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
706
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
802

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock