hi guys

have a problem. customer currently has a 2.5mm(SWA) RCD protected supply to an outbuilding from TNS supply. They are requesting a 2 way cu be fitted for 2 lights and 3 double sockets ( one external). The supply cable is protected with a 20A type B MCB ( which is correct due to installation method )

now the lighting circuit for outbuilding will be protected by a 6A type B MCB as usual and i would usually protect the radial sockets with a 20A type B MCB as per OSG standard circuits.

my problem lies in the fact that there is no discrimination between the 20A supply MCB and the 20A MCB protecting the radial sockets. Is this acceptable within regs or should the supply cable be increased to 4mm 0r 6mm (30/32AMCB)



many thanks any help appreciated
 
There is nothing to stoping you doing a A3 radial and fiting a 16amp breaker or even a 10amp breaker if you wish, you will need to identify what the client intends to use the sockets for.

If it is just for a few power tools, perhaps a kettle or a small fan heater for the winter, then 16amps will be fine. If he intends to plug in welders, piller drills, lathes and such then he will need to redesign the installation to suit.
 
thanks for your reply no the heaviest load will be a lawn mower no heavy loading at all. i thought about reducing the mcb for the sockets to 16A which would be fine for one socket (13A) but there are 3 double sockets and the OSG states 20A minimum. unless im mistaken.
 
Remember Ian the OSG is a GUIDE and what both Mogga and I suggest is a safer circuit than the guides A3 20amp 2.5mm as you are fitting a smaller protection device to a 2.5mm cable, so your erring more on the side of caution.
 
yes malcom i agree, a 16A is safer option than a 20A on a cable (2.5mm) rated at just over 20 A . i have taken the 20A as a min from the OSG rather than as a max as stated by mogga. manythanks guys least the quotes alot cheaper now,
 

Reply to 20a MCB supplying a 20A radial (DB2) in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock