- Reaction score
- 2
Hi all,
Been browsing these forums for a while, always great to learn a new way to skin the same cat.
Anyway, cut a long story short, was an apprentice for a top spark, he packed it in for a new 7 figure income career. I then took a break thinking I should do the same, then I realised not everyone has what it takes to be in the big earner society, so I'm now back, and working for a much older spark.
Thing is, my new boss works with live wires like its perfectly fine, sure he's all PP'd up, but my last boss was ---- about turning everything off, would even walk away from jobs if he couldn't cut-off. I'm in the process of deciding if I should stay with him or move on, or maybe I just need to grow some more chest hair, but thats another story. I guess this is just an age thing, current boss is from a different era.
Now below follows what I've noticed he has done on 2 jobs now and I never seen it done this way before and it has been driving my mind in circles so thought I'd ask and see what others think >
TT supply... Distribution board feeds subs, ie. db is outside in a remote location next to the supply and swa's from db feed all subs (house, garage, outbuilding, guest house, ev charge points etc)
At the db, on outgoing circuits he's using 300ma type-a RCCBs followed by 22x58 fuses on the line, then swa out to sub, where needed he drops type-b 300ma for ev chargers (a pretty penny!). Now he also has a habit of double boxing, ie terminates cw glands on ip68 aluminium boxes inside abs/pc boxes with conduits running into sections of square pvc pipe plumbed into the plastics boxes then all sealed up etc., definitely way more overkill compared to what I've been used to.
What gets me is he says he uses fuses for selectivity, and not mcbs because they'll potentially trip and shut off power to everything at the subs, however I thought you are supposed to use MCBs with RCCBs, I've never seen a fuse being used in front of one before, what am I missing? and wouldn't the fuse blow? which then means square one again but an even bigger hassle for the client? though he says they don't blow that easy with a good mcb doing its job downstream?
Been browsing these forums for a while, always great to learn a new way to skin the same cat.
Anyway, cut a long story short, was an apprentice for a top spark, he packed it in for a new 7 figure income career. I then took a break thinking I should do the same, then I realised not everyone has what it takes to be in the big earner society, so I'm now back, and working for a much older spark.
Thing is, my new boss works with live wires like its perfectly fine, sure he's all PP'd up, but my last boss was ---- about turning everything off, would even walk away from jobs if he couldn't cut-off. I'm in the process of deciding if I should stay with him or move on, or maybe I just need to grow some more chest hair, but thats another story. I guess this is just an age thing, current boss is from a different era.
Now below follows what I've noticed he has done on 2 jobs now and I never seen it done this way before and it has been driving my mind in circles so thought I'd ask and see what others think >
TT supply... Distribution board feeds subs, ie. db is outside in a remote location next to the supply and swa's from db feed all subs (house, garage, outbuilding, guest house, ev charge points etc)
At the db, on outgoing circuits he's using 300ma type-a RCCBs followed by 22x58 fuses on the line, then swa out to sub, where needed he drops type-b 300ma for ev chargers (a pretty penny!). Now he also has a habit of double boxing, ie terminates cw glands on ip68 aluminium boxes inside abs/pc boxes with conduits running into sections of square pvc pipe plumbed into the plastics boxes then all sealed up etc., definitely way more overkill compared to what I've been used to.
What gets me is he says he uses fuses for selectivity, and not mcbs because they'll potentially trip and shut off power to everything at the subs, however I thought you are supposed to use MCBs with RCCBs, I've never seen a fuse being used in front of one before, what am I missing? and wouldn't the fuse blow? which then means square one again but an even bigger hassle for the client? though he says they don't blow that easy with a good mcb doing its job downstream?