hi guys
have a problem. customer currently has a 2.5mm(SWA) RCD protected supply to an outbuilding from TNS supply. They are requesting a 2 way cu be fitted for 2 lights and 3 double sockets ( one external). The supply cable is protected with a 20A type B MCB ( which is correct due to installation method )
now the lighting circuit for outbuilding will be protected by a 6A type B MCB as usual and i would usually protect the radial sockets with a 20A type B MCB as per OSG standard circuits.
my problem lies in the fact that there is no discrimination between the 20A supply MCB and the 20A MCB protecting the radial sockets. Is this acceptable within regs or should the supply cable be increased to 4mm 0r 6mm (30/32AMCB)