I have a 3 phase element for a steam generator but the element is a 220 volt element. the diagram is in Chinese which i cant read. on the diagram it shows three phase delta connection for 380v and three phase star connection for 220 volt with a neutral connected to the star point. My question is can I connect the three phase as is to the element meaning there will be 230v phase to neutral and 400 phase to phase or does the voltage need to be stepped down to 110 volt phase to neutral and 230 volt phase to phase ?
 

Attachments

  • 20220822_101759.jpg
    375 KB · Views: 20
I don't read Chinese either but my initial reaction is that the text showing the alternative element configurations says something like 'for 220V elements connect in star' and 'for 380V elements connect in delta' and that in both cases the supply is taken to be 220/380. You could check the voltage of the control components which would be 220V as they are connected L-N without a transformer.

If the options were for different supplies using the same elements, the voltages on the sketches would be the other way round, i.e. for 380V supply connect in star and for 220V supply connect in delta, but then there would be some provision for adjusting the control supply like a 0-220-380V transformer.

On 400V the element output will be increased by 10% and on 415 by 20%. Normally 380V equipment is OK up to 415 but if it's not conservatively designed it can get a bit warm.

There are online OCR translators that can process images of Chinese text reasonably well, but usually need to be signed up for.
 
Top line of the drawing, it can even convert the image translation into English text

header text.PNG

header text.translated(1).jpg

Coverted to text from picture,

Fully automatic electric heating steam generator three-phase (four-wire) power type wiring diagram
 
I don't read Chinese either but my initial reaction is that the text showing the alternative element configurations says something like 'for 220V elements connect in star' and 'for 380V elements connect in delta' and that in both cases the supply is taken to be 220/380. You could check the voltage of the control components which would be 220V as they are connected L-N without a transformer.

If the options were for different supplies using the same elements, the voltages on the sketches would be the other way round, i.e. for 380V supply connect in star and for 220V supply connect in delta, but then there would be some provision for adjusting the control supply like a 0-220-380V transformer.

On 400V the element output will be increased by 10% and on 415 by 20%. Normally 380V equipment is OK up to 415 but if it's not conservatively designed it can get a bit warm.

There are online OCR translators that can process images of Chinese text reasonably well, but usually need to be signed up for.
yes its got me a bit confused as it seems to be opposite to electric motors which ive always had to connect in delta with a 230V supply and star with a 400V supply... my concern is whether each coil will have 230V across it with the neutral in place or if it will be 400V
 
Yes the crux appears to be this dwg tells you how to use two types of element with different voltage ratings on the same supply, but with motors it's usually telling you how to use the same motor on two different supply voltages. Anything connected L-N will see 230V on a 400/230V system.
 

Reply to 220 volt, three phase element in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
753
How can I convert a 3-phase (220 volt 5.6 kw) pizza oven to 1-phase (220) 2 heating elements, no motor.
Replies
4
Views
1K
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
1K
Hi guys. I was a commissiong technician before I retired. Hardware and software industrial automation. Miss the work but not the endless travel/...
Replies
12
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock