Discuss 230/250 V Contactors Buzzing/Hot in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi.

I've got some lighting & cooker contactors buzzing & overheating..

There are a few old ones in situ with visual thermal damage. coil rated at 250V

I have new ones that are quiet but still warm to touch the sides. coil rated at 230V

I've read that the 230/250 AC coil contactors dont cope well with under/over voltages & perform poorly with slightly too much or too little voltage.

The voltage on the job is at 240V

It certainly feels like its the coils that are heating & moving..

The contactors require being closed full time on the lighting & the cooker contactors need to be closed for 80% of the day, every day.
 
May I ask why you have all this gear with contactors controlling them? Or are you talking about something that aren't contactors as we know them?
 
Is the current rating of the contactors adequate for the loads? Contactors do get warm when energised so should be spaced apart and have some air flow.
 
Last edited:
Hi.

I've got some lighting & cooker contactors buzzing & overheating..

There are a few old ones in situ with visual thermal damage. coil rated at 250V

I have new ones that are quiet but still warm to touch the sides. coil rated at 230V

I've read that the 230/250 AC coil contactors dont cope well with under/over voltages & perform poorly with slightly too much or too little voltage.

The voltage on the job is at 240V

It certainly feels like its the coils that are heating & moving..

The contactors require being closed full time on the lighting & the cooker contactors need to be closed for 80% of the day, every day.
Dell have you put an amp meter on it and what’s the HP
 
Is the current rating of the contractors adequate for the loads? Contractors do get warm when energised so should be spaced apart and have some air flow.
Good points S, I tend to get warm after a bit of hard graft...
 
Basic AC contactor coils do run quite warm, and the coil wrapper does sometimes get quite brown and crispy with age. Is this what you are interpreting as 'overheating'? If there is limited cooling airflow they will run particularly warm but it may not actually be harmful. If you have multiple contactors of the same type, you can check the coil resistance of a good one and compare any suspect ones (or you can sometimes get the resistance from the mfr's data). Genuinely overheated coils often look properly burnt with the copper showing through, and may have significantly reduced resistance due to shorted turns.

Buzzing is usually caused by dirty, mechanically stiff or worn contactors where the armature does not close completely snug against the coil pole pieces. Sometimes they respond to being cleaned and any rust on the pole faces removed, although replacement is often easier.

Contactors usually operate correctly within normal +/- 10% mains voltage variations. A 230, 240 or 250V coil should be OK on UK mains.
 
On lighting circuits I've worked on where the lights are required more than 12 hrs per day (supermarkets) the contactors were alway Normally closed, so were only energised when the lighting was Off.
 
A better description might be '24/7 except on the occasions they are used to turn the loads off'. In which case if they only provide switching and not a safety function, N/C contactors would be more sensible. Beware units that have N/C contacts of lower rating than the N/O!
 
A better description might be '24/7 except on the occasions they are used to turn the loads off'. In which case if they only provide switching and not a safety function, N/C contactors would be more sensible. Beware units that have N/C contacts of lower rating than the N/O!
The 24/7 circuit is for Em lighting. If I had them on a N/C contactor. How would you suggest switching it from the local lighting circuit when it fails. Ems & lights are on different circuits on the same DB
 
OK an N/C contact may not be the best way forward in that specific case, it was just a general point about control of circuits that are more often energised than not.
 

Reply to 230/250 V Contactors Buzzing/Hot in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Morning - just a photo for info to show what's out there (as if most don't already know!!!) & to reiterate the ignorance of some householders. A...
Replies
32
Views
5K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K
H
As a heating engineer, can my thoughts be indulged here to get your opinions? My thought was this: As I understand it, if you use less voltage...
Replies
11
Views
8K
Heating bloke
H
D
Afternoon all, I'm new here and this is my first post. I recently posted on another forum with a rather long post about a problem in my...
Replies
10
Views
4K
DonaldJ
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock