Discuss 240 Heated Schluter cable problem in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I bought a 240 schluter heated cable, did all the required test. everything passed. Tried 2 new thermostats. The heated cable has a hard time getting past 26-28 degrees Celsius. And its constantly fluctuating in temperature even though its set to 29 permanently.

The electrician i used has it hooked up to 14/2 cable and to a single 15amp breaker. Is this the right wire and/or breaker? Could this be the reason the cable wont fully heat up? also if its wrong, is it dangerous? and whats the solution?

thanks
 
could be that the 14/2 is too small, causing volt drop . you need to measure the voltage at the heater terminals under load.
 

Reply to 240 Heated Schluter cable problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
461
I'm in Raleigh, North Carolina and have a well for my house's water supply. For some reason, pitless adapters, which allow all piping to be run...
Replies
1
Views
320
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
Hello, I’m not an electrician and I have a question in relation to Dimplex Duo300n. Some background information: a couple of months ago I have...
Replies
34
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock