Discuss 3 consumer units off one 3 phase meter. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Evening..Just wondering if it's acceptable to run 3 separate consumer units off one 3 phase meter, I have seen 3 consumer units off 3 meters on a 3 phase supply many times but never off 1 meter?

Cheers
 
Evening..Just wondering if it's acceptable to run 3 separate consumer units off one 3 phase meter, I have seen 3 consumer units off 3 meters on a 3 phase supply many times but never off 1 meter?

Cheers

The principle is the same mate. The only difference is that the 3 phase meter is reading all 3 phases at once.
You would use individual meters if the 3 consumer units were being payed individually.
 
one thing worth considering.

You should have a Main isolation switch that turns off power to entire property.
this is amongst other things for the the emergency services to safely disconnect ALL electricity if they need to.

having 3 separate ones is not a good idea, you can still run 3 single phase Db from a 3 phase supply but they should all have a common point of isolation.
 

Reply to 3 consumer units off one 3 phase meter. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
336
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
742
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
954
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
953

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock