Discuss 3 core feeding 2 lighting circuits sharing a neutral in the UK Electrical Forum area at ElectriciansForums.net

L

Lukerthomas

Hi can any one help please doin some work on a house and one of the problems on the test report is there's a 3 core feeding 2 breakers ( red feeding downstairs lights and yellow feeding upstairs lights) and only the one nuetral. Now if I could rewire it I would cables concreted into the floor and can't find the other end to sort it (old house probably plastered behind a wall) now can I put both lives into one breaker feeding both circuits with one neutral solving the problem as it's now one circuit ( 2 feeds lol) I no probably not but any help would be appreciated
 
Are they the only two circuits in the place? Is the load on each circuit low enough for this to work?

Hi there's a couple other breakers on the board all lighting old rewirable board , is that what you ment? The load should be ok but I haven't measured yet it's on a 5 amp at the mo I think. could I put a 10 amp in on a 1.5 can't remember what max current is for 1.5 will check THANKS FOR REPLY
 
Hi there's a couple other breakers on the board all lighting old rewirable board , is that what you ment? The load should be ok but I haven't measured yet it's on a 5 amp at the mo I think. could I put a 10 amp in on a 1.5 can't remember what max current is for 1.5 will check THANKS FOR REPLY

'Should be ok' ?????
 
Thanks only thing is I'm not the tester and if he pulls me or the client up on it (tester probably won't know) be nice to know if the general Senecas is its ok lol I'll screen shot it so if there's any other opions would be good thanks again
 
Last edited by a moderator:
Thanks only thing is I'm not the tester and if he pulls me or the client up on it (tester probably won't know) be nice to know if the general Senecas is its ok lol I'll screen shot it so if there's any other opions would be good thanks again

You will be testing it and signing your name to it after you have completed the remedials though so it is up to you to make sure it is safe and compliant.
 
I would imagine the three core would go to a junction box under the boards somewhere then two T&Es will be connected to that for the two respective lighting circuits with the common neutral.
So although it's not right I don't think this would give rise to danger due to an 'open neutral' on either circuit- however the best compromise is to put the yellow and red in the same OCPD, how many lights are there in total on the existing set up and are there any multi lamp GU10 spots or anything like that ?
 
I would imagine the three core would go to a junction box under the boards somewhere then two T&Es will be connected to that for the two respective lighting circuits with the common neutral.
So although it's not right I don't think this would give rise to danger due to an 'open neutral' on either circuit- however the best compromise is to put the yellow and red in the same OCPD, how many lights are there in total on the existing set up and are there any multi lamp GU10 spots or anything like that ?

That goes without saying Dave.
 
Hi there's a couple other breakers on the board all lighting old rewirable board , is that what you ment? The load should be ok but I haven't measured yet it's on a 5 amp at the mo I think. could I put a 10 amp in on a 1.5 can't remember what max current is for 1.5 will check THANKS FOR REPLY

Don't forget to use the maximum wattage possible for every lighting point, and derate to known installation methods including Cf if connecting to a BS3036.
 
I would imagine the three core would go to a junction box under the boards somewhere then two T&Es will be connected to that for the two respective lighting circuits with the common neutral.
So although it's not right I don't think this would give rise to danger due to an 'open neutral' on either circuit- however the best compromise is to put the yellow and red in the same OCPD, how many lights are there in total on the existing set up and are there any multi lamp GU10 spots or anything like that ?

You don't think this is dangerous!
What planet are you on?
 
That's the thing I don't no if it's compliant? Also I won't be testing or signing the tester will be coming back to check the work is done then he will be retesting and issuing cert
 
It's not many it's the rear lights of downstairs and 1st floor no gu10s or nothing ye tried finding where it joined off to can't find it anywhere so this is pretty much the option I'm left with! The tester has condemned the way it is in 2 breakers sharing neutral but if I put into one breaker current promitting will it count as one circuit and get away with it?
 
That's the thing I don't no if it's compliant? Also I won't be testing or signing the tester will be coming back to check the work is done then he will be retesting and issuing cert

Maybe you need to check in the regs to see whether it will be compliant or not then ? I would start with the area of the regs that deals with the size of neutral conductors.
 
It's not many it's the rear lights of downstairs and 1st floor no gu10s or nothing ye tried finding where it joined off to can't find it anywhere so this is pretty much the option I'm left with! The tester has condemned the way it is in 2 breakers sharing neutral but if I put into one breaker current promitting will it count as one circuit and get away with it?

Unless the client is prepared to pay for rewiring I'm afraid that's the best you can do. Use a 6 amp B type MCB though,nothing bigger, that will be fine as the lights will never all be on together for any significant time and even if they were you'd be under 6 amps.
 

Reply to 3 core feeding 2 lighting circuits sharing a neutral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
621
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
647
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
439
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
884
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock