P

pete.willerton

I have a 3 phase pump and as many people maybe aware the grundfos 3ph pumps are hard to get hold of and they offer a single phase alternative ..:
So I have a 3ph and earth supply and need a 1ph

I know I could just take two fuse's out but a college has mention about this theory

Line conductor into T1 of the contactor then out the load side and then looped round to T2 and then out the load side to the pump and the neutral in T3 of the contactor and out to the neutral of the pump..
Is this correct ?
It's something to do with the overload not being able to function with only one line conductor ?
 
Yes thats fine - some overloads need to see current balance on all 3 poles or they may treat it as a phase down and not function. You need to check though that the coil is the correct voltage it may have been 400v? Wiring on the control may need alteration if you replace a 400v coil with 230v.
 
Last edited:
We use those pumps on nearly all the sites I look after, never had a problem sourcing them, do you have to use that brand specifically?

As what darkwood has already stated there's a bit to consider, a single phase equvalant motor will run at higher current, will the existing switchgear and cables take it?
 
You don't say whether you have a neutral. If you don't, you won't have the 230v needed for the 230 v motor,

? He can just remove two of the cores from the other end and mark them up as
red as brown,
Yellow as spare
Blue as blue

Then reconnect the blue at both ends as a neutrel.

Why do people try to make this so complicated.

Obviously the circuits protection and o/l will probably need changing though
 

Reply to 3 ph contractor conversion to 1 ph in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
546
When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains...
Replies
16
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
664
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock