Discuss 3 phase conversion to 110 in residential USA in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Moved into remote residential site in USA , devestated 3 years ago by tornado that took house, family and all buildings, poles etc. except well building and barn (where I am living for now) only remaining service is a 3 phase that went to well. For about 6-10 months I need to survive here till I can earn a bit of money and get proper 110 service put back in. This is what I want to know is can I temporairly convert some of this power for lights and power tools, etc to use 110 for my personal use.
3 phase service.jpg
 
Last edited by a moderator:
Rule #1 be very careful! Electricity can and does kill.

If you have a multimeter to measure the voltages that would help, as well as knowing the fuse rating.

Be very careful with a multimeter, as you can get the wrong readings easily and if on the wrong range/terminals (like ohms or amps) then it can explode if not adequately fused. So for electrical work that means the likes of CAT-III or CAT-IV rated:
Here are some examples:
Most meet III rating, many IV.

The wires from those fuses do not look very thick, so the current limit might be quite low. That will determine what you can run from it and for some tools the motor surge might be the limit to be aware of as it can blow fuses on start-up.

For voltages measure from fuse-fuse, and also from fuse to neutral (assuming there is a "cold" terminal for neutral?)

I am UK-based so someone like @Megawatt is far better placed to advise.
 
Moved into remote residential site in USA , devestated 3 years ago by tornado that took house, family and all buildings, poles etc. except well building and barn (where I am living for now) only remaining service is a 3 phase that went to well. For about 6-10 months I need to survive here till I can earn a bit of money and get proper 110 service put back in. This is what I want to know is can I temporairly convert some of this power for lights and power tools, etc to use 110 for my personal use.View attachment 94044
What is your voltage right now so I can help you out. 3 phase on a residential project
 
Looks like a old pump panel, most older ones had no neutral. Years ago had to use a transformer to get temp 120 volt power off a 240V 3 phase 3-wire service for a AG pump, the 3rd leg (high leg) was not even metered. More details are required.
 

Reply to 3 phase conversion to 110 in residential USA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
578
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
My daughter lives in a flat in London in converted circa 1900 5 storey terrace in Bethnal Green. She is considering getting a Stiebel Eltron...
Replies
5
Views
1K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock