Discuss 3 Phase Motor - Insulation Resistance Testing in the Commercial Electrical Advice area at ElectriciansForums.net

Like RoB2 I use 500V followed by 1000V and have done so for the past 40 years. And to be honest with you I see no reason to change my methods.
 
With such small motors that the OP is talking about, 500V IR tests are more than ample. When you start talking about the bigger motors, say from around 5 to 7.5 HP upwards, i can see where Tony is coming from.

Darkwood made good sense in his observation about these motors being suitable for the environment they are being used in. He is probably right too, that these failing motors are not constructed to meet the conditions they are being subjected too. Dampness and humidity has nothing to do with a motors IP rating, that's down to the winding construction. On the HK MTRC system, any motors (normally sump pumps and fans etc,) located in the very humid tunnel sections would have encapsulated windings, among other physical protective measures....
 
Thanks for the replies. Just to clarify, I am not an electician, I am an apprentice, working with people who don't seem to know too much either. Which is why I wanted to ask for some advice more than anything, as I won't be going back to college for a while.

Any test I do is offline, and no power is ever present (as I'm not competent enough yet).

The motors are IP56, but the cleaning people get very enthusiastic, and manage to get water in everywhere it seems!!

So it seems as a rule of thumb, you would IR test at double the rated voltage?

Rob2. You asked why IR test the windings? Mainly as I have been told to, and a recent motor which failed was good to earth between phases, but when tested between 2 windings, it failed. Not the same terminals of the same windings by the way :) So should the windings to windings test be done with an ohm meter, and not a IR Tester?



Also, WHY do you test a motor (small) on 500v? Is there a reason, or is it just because it is double the winding voltage?




Thanks for all the replies.
Ryan
 
You asked why IR test the windings? Mainly as I have been told to, and a recent motor which failed was good to earth between phases, but when tested between 2 windings, it failed. Not the same terminals of the same windings by the way :) So should the windings to windings test be done with an ohm meter, and not a IR Tester?

No, winding to winding tests are IR tests, your checking for insulation breakdown and/or weakness in the insulation between the two windings. Individual winding tests (end to end) are conducted with a low ohm meter. Your typical MFT or multimeter, are not really suitable for accurate results, you really need a bit of current flowing such as you would get with a Ductor Tester set at the right range, or a 4 point low ohm meter...
 
The motors are IP56, but the cleaning people get very enthusiastic, and manage to get water in everywhere it seems!!

At IP 56, the cleaners must be jet washing them individually. If that's the case, the company either needs to have words with these cleaners, or purchase very expensive IP 67 replacements!! lol!!
 
Oh I see. That is what I was testing for, insulation breakdown on the motor windings as the motor had failed.

Then you have done what you have been asked to do then, ...confirmed an insulation breakdown between two windings.
Not much else you can do....
 
Sorry dont think I made myself clear, I thaught you had been IR testing the windings end to end as well as phase to phase.

As E54 has said just a low ohm meter will not show up all faults testing windings end to end, but if the results per winding are different it usually indicates something unterward.

I've said on post#19 how I would IR a motor although others will disagree on my methods. Testing at 500v I'd done as it's above the operating voltage of the motor, testing at lower than the rated voltage isn't putting enough pressure into the circuit to show a possible fault.

And as for why it's 500v, it's an industry standard.
 
At IP 56, the cleaners must be jet washing them individually. If that's the case, the company either needs to have words with these cleaners, or purchase very expensive IP 67 replacements!! lol!!

I've used jet washers in the past that would instantly strip the paint off motors, forget IP67, water gets everywhere
 
I meant to say IP 68, lol!!

Doesn't matter if you strip the paint off them, you shouldn't be able to get water past that degree of protection, into electrical parts that will be detrimental to it's running.... Not at the price they normally charge for such motors anyway....lol!!!
 

Reply to 3 Phase Motor - Insulation Resistance Testing in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
578
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
746
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock