Discuss 3-Phase question - industrial unit in the Industrial Electricians' Talk area at ElectriciansForums.net

Alex C2

DIY
Reaction score
0
Hi

Hoping someone knowledgeable can give me an idiots guide to power for an industrial unit we are leasing. Please bear in mind I have close to zero electrical knowledge.

We need 3-Phase power 400V connections for around 6 drilling systems we run on an intermittent basis, no more than 2 running at the same time. The small systems can draw 32A at peak but for a few seconds max, the air compressor is a 11Kw motor and runs intermittently to keep up the pressure in a small run of pipe work, obviously more often when pneumatic hand tools are running. The premises when I viewed it initially had around 8 400V plug sockets dotted around the periphery - ideal. They were however removed on the completion of the unit re-furb, and we need to put some back in on the fit-out.

When I enquired with the distribution co. about the incoming supply, I was told it was "60Kva 3-Phase, 20Kva per phase". The electrician we have on the fit-out works states that this is way too low "86A to site, 28A per phase" and cant be right for a 6500SQ ft industrial building. It is a worry for me as we expected based on what was there previously to have sufficient supply, I could only get information form the ElecNW after becoming the lease holder.

I have very little understanding of electrics unfortunately, so i'm not sure why the figure stated seems to be perceived as too low, and also if it is realistically too low for our needs.

Anyone who can give an opinion and help me calculate if we have a problem is most welcome!
 
His sums are wrong. 20Kva is 20,000. Divide that by 230v single phase and you get the 86A but that’s PER PHASE.
If you can see the incoming cable head, there will be 3 supply fuses. These will have a rating on a sticker somewhere. Generally 63A, 80A or 100. Could be as much as 200 for an industrial unit. Again that’ll be per phase.
 
I'm based in Cheshire. can sort it all out for you. and that "electrician" is talkingout of his arse, 20kVA per phase is 86A per phase. should be plenty for what you want.
[automerge]1569580056[/automerge]
arrrghh. beaten by a Jock.i'll never live it down. serves me right for putting 40 alloy wheels on ebay.
 

Reply to 3-Phase question - industrial unit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
581
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
335
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
953

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock