Discuss 3 phase RCD question in the UK Electrical Forum area at ElectriciansForums.net

It did look odd as I typed it and had to retrace my steps to convince myself that I hadn't overlooked something. Consider three identical resistive loads connected in star to form a perfectly balanced 3-phase 3-wire load. Everything is perfectly insulated from earth, so cannot produce any earth leakage / RCD differential current. The three currents at the load star point vectorially sum to zero and the star point will take up the same voltage as the supply neutral. Therefore it doesn't matter whether the star point is connected to neutral or not; no current will flow along the neutral conductor because there's no potential difference between the load star point and the supply star point.

If protective earth and neutral are at the same potential, then the same is true of a connection between the star point and earth. The star point could be solidly connected to the system CPC without producing earth-leakage. If we consider that the CPC has zero resistance, the three single-phase loads could be separately connected to their own CPCs without creating differential current upstream of their interconnection point, because although there are now currents circulating through the CPC they still sum to zero.

With ideal components there's no limit to the total symmetrical leakage that could be accommodated, but in the real world there are so many sources of asymmetry that one probably can't get away with very much. One should perhaps assume that only a total leakage less than I-delta-N is acceptable for practical use, but might nonetheless find that exceeding this limit doesn't always cause a trip.

Also worth noting on a different subject that for real loads such as transformers and motors, the internal star point is generally not connected to neutral to prevent circulating currents due to asymmetry; it is not true in practical applications that zero potential exists between the supply and load star points.
Thank you, yes, I hadn’t thought of it as a floating star point.
 

Reply to 3 phase RCD question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
378
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
770
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
860
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
315

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock