Discuss 3 phase voltage drop calculation? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi!

Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right?

For example: three phase 30kW appliance, 10mm 90 degree SWA, 45 meter run.

30,000/sqrt3/400 = 43.3A = Ib
from the table 4E4B, a 10mm cable gives 4.7
So then 43.3 x 4.7 x the 45 meter run gives = 9157.95 mV
gives 9.157 V
9.157/400 = 0.02289 = 2.289% voltage drop

Is that right?

Thanks!

Ben
 
Hi!

Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right?

For example: three phase 30kW appliance, 10mm 90 degree SWA, 45 meter run.

30,000/sqrt3/400 = 43.3A = Ib
from the table 4E4B, a 10mm cable gives 4.7
So then 43.3 x 4.7 x the 45 meter run gives = 9157.95 mV
gives 9.157 V
9.157/400 = 0.02289 = 2.289% voltage drop

Is that right?

Thanks!

Ben
Sorry - 4.0 from the table! But - still - how's the working?!
 
Sorry - 4.0 from the table! But - still - how's the working?!
You do not divide the voltage by the the drop. The drop as you have calculated it, is accurate & you must now compare that it's within the limits permissible, which is 5% for power circuits ( 3% for lighting).
5% of 400v is 20v. Your circuit is within the limits with enough to spare for any additional Vd if your circuit is supplied from a secondary distribution board.
 
Hi!

Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right?
Yes
For example: three phase 30kW appliance, 10mm 90 degree SWA, 45 meter run.

30,000/sqrt3/400 = 43.3A = Ib
Correct
from the table 4E4B, a 10mm cable gives 4.7
No, it should be 4.0 from column 4 as you are looking for the three-phase drop.
So then 43.3 x 4.7 x the 45 meter run gives = 9157.95 mV
gives 9.157 V
9.157/400 = 0.02289 = 2.289% voltage drop

Is that right?
Almost, you would be looking at:
43.3 * 4.0 * 45 = 7.79V
Then percent drop is 7.79V / 400V = 1.95%
 
No It isn't correct! You do not divide the Line to Line voltage by the voltage drop!

Why would you? The voltage drop is per individual cable & since when do you run 3 phases through 1 cable? You have already factored in the additional phases when working out Ib. (design current)
 
No It isn't correct! You do not divide the Line to Line voltage by the voltage drop!

Why would you? The voltage drop is per individual cable & since when do you run 3 phases through 1 cable? You have already factored in the additional phases when working out Ib. (design current)
Because the VD values given in the related column are for that case.

The alternative is to consider 3 pairs of single phase cables, for which you would have:

VD = 43.3 x 4.7 x 45 = 9.157 V = 9.157 / 230 = 3.98%

Now as it is actually a balanced 3-phase load the neutral currents cancel, so you only get drop in the line conductors and thus half the percentage drop in total = 3.98 / 2 = 1.99%

Given that column 3 and column 4 in Table 4E4B are only quoted to 1 significant digit (from 0.1/4.0 = 2.5% etc) you see the approaches both give the same answer of around 1.9-something (as 1.95 * 1.025 = 1.99875 etc)
 

Reply to 3 phase voltage drop calculation? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
377
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
806
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
790
First, I really appreciate any feedback you can provide. Its awesome to have a group of people that have a passion for this! Our RV Park has a...
Replies
20
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock