A quick check of the cable resistance values (Prysmain BS5467 data sheet) has R1 for 16mm as 1.15 mOhm/m and R2 as 3.1 mOhm/m, paralleling the conductors leads to R1+R2 of about 3.68 mOhm/m so for the 185m run around 0.68 Ohms.

For a 16A MCB that is usable to D-curve.

But for a 32A MCB that already (even before looking at the supply DB Zs) puts the supply MCB limit at a B-curve, and that might be too trip-happy on the machine's start up current.

So you might be looking at a 100mA delay RCD to meet sub-main disconnection times (unless you look at a 32A or 40A switched-fuse, etc)
 
We seem to have lost our way on this thread, the OP wants 32amps single phase from a 16amp/P three phase supply, or is it me that's lost the plot?
 
We seem to have lost our way on this thread, the OP wants 32amps single phase from a 16amp/P three phase supply, or is it me that's lost the plot?
Well, the issue was feeding a 32A single-phase load from the end of a long 3-phase cable that only meets VD, etc, for 16A.
  • Converting 3P => 1P via transformer(s) of VFD is one route, but not cheap,
  • Reconfiguring 4C 16mm to avoid a new sub-main is another possibility, but loss of 3P options
  • Or the simple, obvious, but potentially expensive iv civil work needed to put in a dedicated 1P 31A feed.
  • Possible, but maybe not feasible for cost, difficultly & warranty reasons, etc, would be to convert the load to use a 3P motor, etc.
Any other options?
 
Was first in list, 3P->1P conversion.

I did look at the site, but it sucks in terms of finding stuff. They did list a 1P -> 1P VFD but I did not see 3P -> 1P mentioned. Do you know of a part?

I know some "3 phase" UPS are really 3P charger, 1P inverter (you can tell as they tell you on bypass the L1 needs 63A instead of the 25A MCB for the L2/L3), but they are hardly a cheep option.
 
When I bought from Invertek the site was much easier to navigate they seem to have retro graded the site somewhat, used to have a list down the left side of all the drives they had available, I can't find a link to even the one I have let alone a 3P->1P conversion.
 
Hi, OP here - sorry for the disappearing act, I've been on 16 Hr days building even more sheds for an upcoming job. All great ideas, will digest and respond over the weekend. Thanks all.
 
Thanks again for all the advice.

The machine is some kind of funky super-powerful x-ray machine for scanning vehicles. I don't have the full specs but I have to assume it does need constant current, not just inrush. However, I doubt it would be energised and generating radiation for very long periods.

The rental is only for a couple of weeks for a research project (that’s what I offer here), so there’s no question of digging trenches or otherwise messing with the direct-buried underground infrastructure.

The solution is so obvious I missed it! As several on here said, just temporarily swap a few cables and breakers at each end to single-phase the DB on 2 x 16mm paralleled conductors.

Physically lock off any three-phase breakers in the building’s DB (supplying only a few 5P sockets, and two small roller shutters which can be opened manually.)

Sorted in an hour at zero expense and at least another hundred quid a day on the rental for bespoke 'supply upgrade' ?
 
Completely OT but curiously relevant. After WW2 there was an upsurge in cases of TB and the (then new) NHS launched a 'mass radiography' programme, sending dozens of mobile chest X-Ray screening vans out to hotspots (e.g. industrial towns) to locate cases before people developed symptoms. The X-Ray machines needed a 30A single-phase supply for which they re-purposed diesel generators from redundant Type 14 radar sets. These were actually 3-phase generators but rated to deliver full load on any one phase. They decommissioned the 3-phase outlets and partially rewired the control panels, and off they went around Britain.
 

Reply to 32A single phase output from 3 x 16A three phase supply. Is there a way? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
678
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi everyone, each leakage question here. I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and...
Replies
11
Views
4K
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock