I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine until the next time the heat pump calls for power. I thought it might be faulty so I swopped it out but had the same issue with the new one.

What might cause this to happen?

Thanks
 
Is this a new fault on an existing installation which has previously worked?

Or is it a fault on a new installation/something which has always happened since installation?
 
Sounds like the motor stiffens up when stopped, then the MCB hits the magnetic on first start, but draws that little bit less on the subsequent starts.
mainline's possibly failing capacitor would be worth checking.
 
Then it's likely something is failing in the heat pump.

Was the replacement MCB exactly the same as the old one? Same rating, tripping curve, manufacturer etc?
I replaced it with like for like B rated 32amp. I tried a C rated. Same result. It's a 15Kw heat pump. Should I try a D rated? The max starting current is 74amps.

This is the motor being used. Compressor copeland zr72kce-tfd522, 1.242,61 € - https://www.skh-kaeltetechnik.de/Compressor-Copeland-Emerson-ZR72KCE-TFD522
 
Last edited:
This is a 3 phase motor, so presumably a 3 pole MCB. I think most of us had assumed single phase.
Won't be any capacitors or start windings.
Possibly one faulty phase winding? Check the currents in each phase for balance, with a clamp meter
 

Reply to 32Amp MCB tripping initially and then staying on when pushed back up? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
642
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
674
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
854
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock