santidreamer

I need to buy a 3 phase HV transformer for an apartment block

1382 Amps is the total predicted single phase load after diversity.

1 Phase KW
1382 Amps
230 Volts ( I/V)
317.86 KW

KW 1 Phase KW to KVA

317.86 KW
0.9 Power factor ( KW x P.F. = KVA)
353 KVA

KVA Single Phase to 3 phase conversion
KW = V x I x 1.73/ 1,000
1382 Amps
Divide total load by 3 load per phase
460 Amps per phase
400V
1.73root 3
319 KW

3 Phase KW to KVA
318.KW
0.9Power Factor (KW x P.F. =KVA)
354.KVA

So 500KVA transformer. Needed
 
Last edited by a moderator:

Reply to 350 KVA HV Transformer? 3 phase calculation confusion in the Australia area at ElectriciansForums.net

Similar Threads

I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi Everyone May be someone could shed some insight on the sizing and provide some suggestions: 3 phase Generators (400 V, 50 Hz) have the...
Replies
4
Views
2K
Hello everyone, I really hope this isn't an idiot question but boy, I'm out of my depth! I've spent about 3 weeks (not solid mind) trying to work...
Replies
13
Views
2K
Hi Everyone I would be glad if you could clarify this for me: For a Load Estimate Survey whereby 95% is single phase, the Load Estimate is 90...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock