Discuss 3ph to domestic property, 80A or 100A? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Customer has asked for DB and new CUs for large dwelling house, WPD are putting in 3 phase to replace 100A single phase and are saying fit 80A main fuses....

Main load on all phases is Tesla wall charger 32A and a ground source heat pump 32A.

Given they are both loads that will run potentially continuous duty cycle, that's 64A, leaving 16A headroom per phase.

There are 2 CUs one with 3 RMs and one for a bunch of lighting circuits. Presuming I wire each CU to a separate phase, that's still not going to be enough unless WPD put in 100A main fuses?

Options, please!

1) Leave the existing 100A single phase in and have 2 meters?
2) Insist they install 100A supply/fuses? That's still only a 36A supply after the two big loads.
3) Split the RM CU and have different floors on different phases? Maybe even add a 3rd CU on L3?

Thx! :)
 
There are 2 CUs one with 3 RMs and one for a bunch of lighting circuits. Presuming I wire each CU to a separate phase, that's still not going to be enough unless WPD put in 100A main fuses?
Is it the 3 RM that you are concerned by? The On Site Guide Appendix A table from domestic final circuts has 100% of the largest circuit + 40% of the remainder, say, 32 + 0.4*(2*32 + 3*6) = 65A
 
65A load for a domestic house? Only if they're growing weed!
True, it seems way too high for any sane activity, but in terms of diversity versus total listed CU circuits it is at least justifiable!
[automerge]1588004200[/automerge]
Actually the lighting should be separate and have a 0.66 factor.
3 RM & 3 lights = 32 + 0.4 * (2*32) + 0.66*(3*6) = 69A and still higher than sane!
But better than 114A
 
is the heat pump existing?
if not, I would suggest a 3phase unit.

can you put in a 3 phase db adj. meter with a feed out to each of the house db's and separate feeds to the big loads (charger and heating etc.)

this will alow you to balance the phase currents as best you can.
 
True, it seems way too high for any sane activity, but in terms of diversity versus total listed CU circuits it is at least justifiable!
[automerge]1588004200[/automerge]
Actually the lighting should be separate and have a 0.66 factor.
3 RM & 3 lights = 32 + 0.4 * (2*32) + 0.66*(3*6) = 69A and still higher than sane!
But better than 114A

How
is the heat pump existing?
if not, I would suggest a 3phase unit.

can you put in a 3 phase db adj. meter with a feed out to each of the house db's and separate feeds to the big loads (charger and heating etc.)

this will alow you to balance the phase currents as best you can.

Acvpridng to the OP it is a three phase car charger and a 3 phase heat pump
 

Reply to 3ph to domestic property, 80A or 100A? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
I've been volunteering at my local village hall, installing audio and light systems. Converting what was originally an underused sports hall into...
Replies
68
Views
6K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock