- Reaction score
- 8,777
At a bread and butter job, loose socket, socket not working, change two lights.
Sticking out rather like a sore thumb was this (I removed the wire to check size):
I finished the other work, then said could I have a look at the shower as I've got a concern.
It was 8.5kw shower. 6 sq mm cable at shower (new colours). 6 sq mm cable at isolator, feed was old colours.
Customer added that the isolator had been moved a long while ago. I stopped short of probing around the loft for a joint box.
Current shower was fitted 3 years ago, they never got a MWC in spite of wanting one.
My assumption is it was once a B32 and a lower rated shower.
It's been there 3 years, no signs of thermal damage. CU is in a former garage so possibility cable is clipped direct.
What would your comment to customer have been? (I may show the customer this thread so I won't say what happened yet)
Sticking out rather like a sore thumb was this (I removed the wire to check size):
I finished the other work, then said could I have a look at the shower as I've got a concern.
It was 8.5kw shower. 6 sq mm cable at shower (new colours). 6 sq mm cable at isolator, feed was old colours.
Customer added that the isolator had been moved a long while ago. I stopped short of probing around the loft for a joint box.
Current shower was fitted 3 years ago, they never got a MWC in spite of wanting one.
My assumption is it was once a B32 and a lower rated shower.
It's been there 3 years, no signs of thermal damage. CU is in a former garage so possibility cable is clipped direct.
What would your comment to customer have been? (I may show the customer this thread so I won't say what happened yet)