Discuss 4mm2 for 32A in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi,

I have an incoming 32A single phase supply to a 16A equipment. To protect the equipment I installed a 16A MCB in between.
My question is for the cable from 32A MCB to 16A MCB, can I use 2+e x 2.5mm2 cable?

I know for 32A we are supposed to use 4mm2 cable, but the electrical shops nearby only sell cable in bulk, and I only have 2.5mm2 cable with me, so I wonder if 2.5mm2 is sufficient, since the 16A MCB will cut off when current exceed so, and in daily operation the current is less than 16A.
The 2.5mm2 cable will be less than 1 meter, freely hang along the wall indoor. Cable type is H07RN-F.

Thank you very much!
 
The 16 amp MCB will protect the short run of cable from the supply.
 
Hi,

I have an incoming 32A single phase supply to a 16A equipment. To protect the equipment I installed a 16A MCB in between.
My question is for the cable from 32A MCB to 16A MCB, can I use 2+e x 2.5mm2 cable?

I know for 32A we are supposed to use 4mm2 cable, but the electrical shops nearby only sell cable in bulk, and I only have 2.5mm2 cable with me, so I wonder if 2.5mm2 is sufficient, since the 16A MCB will cut off when current exceed so, and in daily operation the current is less than 16A.
The 2.5mm2 cable will be less than 1 meter, freely hang along the wall indoor. Cable type is H07RN-F.

Thank you very much!
Carp
 
Why not have the 32A mcb changed to 16A?
If we are talking wiring that forms part of the fixed electrical installation then no, a single 2.5mm cable will not be protected by a 32A mcb.
 
It would seem strange not to look at simply changing the supply to 16A as easier than a 2nd MCB.

The answer as to whether or not your system is protected is not that simple. While the 16A MCB near the load should protect against overload, you should still verify that in the event of a fault on the cable(s) they are protected by the 32A MCB.

That means a check the the E conductor is large enough to meet the adiabatic limits for fault-clearing on a 32A MCB, and that the fault impedance at the end of the 32A section is low enough that it would still disconnect in under 0.4s
 
Why not have the 32A mcb changed to 16A?
If we are talking wiring that forms part of the fixed electrical installation then no, a single 2.5mm cable will not be protected by a 32A mcb.

Protected from overload?

That will be via this, that will:
I installed a 16A MCB in between.

Protected from fault current?

Do we really need to do adiabatic calculations for a 1m length of cable rated at 27A on a B32?

If this were a ring final with an unfused 2.5mm² spur supplying a DSO would you really object that the cable was not protected?
 
Last edited:
That means a check the the E conductor is large enough to meet the adiabatic limits for fault-clearing on a 32A MCB, and that the fault impedance at the end of the 32A section is low enough that it would still disconnect in under 0.4s
Loop tests at the new socket yes, but how many people carry out adiabatic checks when installing this:

1617746960020.png


?
 
Do we really need to do adiabatic calculations for a 1m length of cable rated at 27A on a B32?
Reading it again, not really.

Initially I was thinking of T&E with the smaller E conductor but reading it again it seems to be 2.5mm H07RN-F which of course has a 2.5mm E. Also the short length means it should not have any disconnection issues.

Only real comment about that would be using ferrules as usually MCB terminals are not designed for fine-stranded cable.
 
Loop tests at the new socket yes, but how many people carry out adiabatic checks when installing this:
Odd, your new post is saying "Yesterday at 11:09 PM"!

That is true, and a quick check in the OSG for Table B7 it has 1.5mm (i.e. T&E CPC size) as safe for all typical MCBs to 40A B/C curve provided the PFC is below 3kA which is probably the vast majority of cases.
 
So short answer is fine for 2.5mm feeding 16A MCB, but remember the ferrules for fine stranded flex.

But just odd not to simply change the supply MCB (though if odd make, etc, might be harder to do)!
 

Reply to 4mm2 for 32A in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fitting a a couple loft sockets on a radial circuit. I only have 2.5mm cable and really don’t want to buy a reel 4mm2 is it ok to use on 32A...
Replies
10
Views
2K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
576
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Hi all, Our kitchen is going to be ripped out and replaced in the new year, and currently has just one small oven in it - I have 10 guests for...
Replies
26
Views
3K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock