Discuss £5,000 Electricity Bill!!!!!! in the UK Electrical Forum area at ElectriciansForums.net

At £0.14 per Kw hour this property has use over 35,700 Kw and means they are using over 16 Kw per hour every hour! What the hell are they feeding? The factory next door???
 
At £0.14 per Kw hour this property has use over 35,700 Kw and means they are using over 16 Kw per hour every hour! What the hell are they feeding? The factory next door???

That's what I thought, too. Sometimes we see these threads and it's fairly easy to predict something like an immersion heater etc, but THAT amount of power just doesn't compute. There HAS to be either an error in measurement or a DNO/construction level cabling fault.

If the OP is still reading this thread, go into Maplins and spend £20 on an AC CURRENT CLAMP METER. Put the jaws around either one of the cables that go FROM the meter into the fusebox, set the dial to 'A' (not mA) and tell us what the numbers are.
 
That's what I thought, too. Sometimes we see these threads and it's fairly easy to predict something like an immersion heater etc, but THAT amount of power just doesn't compute. There HAS to be either an error in measurement or a DNO/construction level cabling fault.

If the OP is still reading this thread, go into Maplins and spend £20 on an AC CURRENT CLAMP METER. Put the jaws around either one of the cables that go FROM the meter into the fusebox, set the dial to 'A' (not mA) and tell us what the numbers are.
eh?....a `20 quid` current clamp with mA on it.......i`l have one please...
 
eh?....a `20 quid` current clamp with mA on it.......i`l have one please...

Can't be 100% sure, but pretty confident my last cheap 'drop in the mud' one was less than £30
 

Reply to £5,000 Electricity Bill!!!!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
I have a question for you all, We recently moved, and the old house had the analog meter on it, the new place has 3 structures on the property.. a...
Replies
10
Views
3K
I have a three phase supply in my house in Azerbaijan. The incoming cable from the meter is 4x35mm SWA with a 120A DNO breaker, CU is a Schneider...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock