Discuss 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

It's no good people shouting about how a cable should be ok because the shower "should" only on for 10 mins. It's either suitable for the OCPD or it's not for goodness sake.
Really can't see what the argument is.
 
Agree with richard , showers rarely used longer than 5-10 mins , too short a time for cable to heat up.

Some people like to have sex in the shower. Could upset your 5-10minute rule. They would have to get out every 20 mins to turn the mcb back on. Dangerous with wet hands hurrying to get back:rolleyes2:
 
I was always of the understanding, the higher the kw rating of the shower, doesn't mean it gets hotter, just allows more water to flow at the required temperature.
The lower the power rating the less amount of energy it has to heat the water so it flows slower to maintain the temperature.
 
remember a few years back one of the sheds was doing 10.5kw showers for about £45 well a bloke fitted one on 6mm replacing his old 7.5kw cable ran on outside wall of house and it melted it from one end to the other,guy was well peed off.asked for a price and said the cost of cable alone was more than cost of shower,got quite funny about it so I told him that my shower worked fine so either way it didnt bother me if he had it fixed or not.lol
 
remember a few years back one of the sheds was doing 10.5kw showers for about £45 well a bloke fitted one on 6mm replacing his old 7.5kw cable ran on outside wall of house and it melted it from one end to the other,guy was well peed off.asked for a price and said the cost of cable alone was more than cost of shower,got quite funny about it so I told him that my shower worked fine so either way it didnt bother me if he had it fixed or not.lol

Nice answer haha. Not your fault his DIY went belly up!
 
I was always of the understanding, the higher the kw rating of the shower, doesn't mean it gets hotter, just allows more water to flow at the required temperature.
The lower the power rating the less amount of energy it has to heat the water so it flows slower to maintain the temperature.


Indeed mate, higher rating means better flow as power is fixed and temp is controlled by throttling water flow. Downside of a lower rated shower is on a winters morning when the water entering the unit isn't much above freezing... :christmaswindow:
 
9.5KW shower at 240V takes 39.6A

9.5KW shower takes 37.9A at 230V

40A Circuit Breaker will hold indefinitely for a 9.5KW shower.

Will not trip what ever you have to do in the shower.
 
9.5KW shower at 240V takes 39.6A

9.5KW shower takes 37.9A at 230V

40A Circuit Breaker will hold indefinitely for a 9.5KW shower.

Will not trip what ever you have to do in the shower.

The debate is that some people believe 6mm cable is adequate for a 40A MCB, not that a 40A MCB is ok for a 9.5 kw shower.
 
Supply Voltage = 230 Volts

Power factor = 1

Ib - Design current = 41.3 Amps

Protective Device Type = MCB type B (BS EN 60898)

In - Protective Device Rating = 45 Amps

Cable Type : Twin & Earth

Length of run of cable = 10 metres

Installation Method : Single-core or multicore cable direct in masonry having a thermal resistivity

not greater than 2 K.m/W - without added mechanical protection.

(method C)

Ambient temp = 30 °C

Number of circuits including this one = 1

Length of cable in thermal insulation = none

Apply Correction factors:

From TABLE 4C1 : Cg = 1 (Grouping)

From TABLE 4B1 : Ca = 1 (Ambient temp)

From TABLE 52.2 : Ci = 1 (Insulation)

Protective device factor for Buried cables : Cc = 1

Cd = 1

Cs = 1

Protective device factor : Cf = 1

It = tabulated current carrying capacity

It = In / (Cg x Ci x Ca x Cf x Cc x Cs x Cd)

It = 45 / (1 x 1 x 1 x 1 x 1 x 1 x 1 )

It = 45.00 Amps

From TABLE 4D5 Cable selected = 6 mm²

Current capacity of cable selected = 47 Amps

TABLE 4D5 For 6 mm²: mV/A/m = 7.3

mV/A/m corrected for power factor = mV/A/m x Power Factor = 7.3 x 1 = 7.3

Voltdrop = (mV/A/m x Length x Design current) / 1000

Voltdrop = ( 7.3 x 10 x 41.3 ) / 1000

Voltdrop = 3.01 Volts

(Maximum permissible voltdrop (regulatuon - 525) = 11.5 Volts)

Calculated Cable size = 6 mm², Actual Earth conductor size = 2.5 mm²

Maximum Cable Length = 38.1 Metres
 
Supply Voltage = 230 Volts

Power factor = 1

Ib - Design current = 41.3 Amps

Protective Device Type = MCB type B (BS EN 60898)

In - Protective Device Rating = 45 Amps

Cable Type : Twin & Earth

Length of run of cable = 10 metres

Installation Method : Single-core or multicore cable direct in masonry having a thermal resistivity

not greater than 2 K.m/W - without added mechanical protection.

(method C)

Ambient temp = 30 °C

Number of circuits including this one = 1

Length of cable in thermal insulation = none

Apply Correction factors:

From TABLE 4C1 : Cg = 1 (Grouping)

From TABLE 4B1 : Ca = 1 (Ambient temp)

From TABLE 52.2 : Ci = 1 (Insulation)

Protective device factor for Buried cables : Cc = 1

Cd = 1

Cs = 1

Protective device factor : Cf = 1

It = tabulated current carrying capacity

It = In / (Cg x Ci x Ca x Cf x Cc x Cs x Cd)

It = 45 / (1 x 1 x 1 x 1 x 1 x 1 x 1 )

It = 45.00 Amps

From TABLE 4D5 Cable selected = 6 mm²

Current capacity of cable selected = 47 Amps

TABLE 4D5 For 6 mm²: mV/A/m = 7.3

mV/A/m corrected for power factor = mV/A/m x Power Factor = 7.3 x 1 = 7.3

Voltdrop = (mV/A/m x Length x Design current) / 1000

Voltdrop = ( 7.3 x 10 x 41.3 ) / 1000

Voltdrop = 3.01 Volts

(Maximum permissible voltdrop (regulatuon - 525) = 11.5 Volts)

Calculated Cable size = 6 mm², Actual Earth conductor size = 2.5 mm²

Maximum Cable Length = 38.1 Metres


Haha!! I wondered if someone couldn't resist posting the calculation !!

Just out of interest, I would have thought there was a good chance of some cable Grouping (Cg) at some point on the run but i know not always - the original post didn't specify either way. If in doubt i always assume there must be a few cables running together! Just one cable along side would take the requirement above 50A - just a thought!
Also, are there many MCB manufacturers who make a 45A Type B MCB now? If only 50A MCB available then 6mm again, no good.
Thought most modern boards (17th edition etc) only give the options of 40A & 50A. Only seen 45A on old Wylex breakers. You know anyone who supplies 45A MCB's with new RCD boards - be interesting to know for future reference!!??
 
Supply Voltage = 230 Volts

Power factor = 1

Ib - Design current = 41.3 Amps

Protective Device Type = MCB type B (BS EN 60898)

In - Protective Device Rating = 45 Amps

Cable Type : Twin & Earth

Length of run of cable = 10 metres

Installation Method : Single-core or multicore cable direct in masonry having a thermal resistivity

not greater than 2 K.m/W - without added mechanical protection.

(method C)

Ambient temp = 30 °C

Number of circuits including this one = 1

Length of cable in thermal insulation = none

Apply Correction factors:

From TABLE 4C1 : Cg = 1 (Grouping)

From TABLE 4B1 : Ca = 1 (Ambient temp)

From TABLE 52.2 : Ci = 1 (Insulation)

Protective device factor for Buried cables : Cc = 1

Cd = 1

Cs = 1

Protective device factor : Cf = 1

It = tabulated current carrying capacity

It = In / (Cg x Ci x Ca x Cf x Cc x Cs x Cd)

It = 45 / (1 x 1 x 1 x 1 x 1 x 1 x 1 )

It = 45.00 Amps

From TABLE 4D5 Cable selected = 6 mm²

Current capacity of cable selected = 47 Amps

TABLE 4D5 For 6 mm²: mV/A/m = 7.3

mV/A/m corrected for power factor = mV/A/m x Power Factor = 7.3 x 1 = 7.3

Voltdrop = (mV/A/m x Length x Design current) / 1000

Voltdrop = ( 7.3 x 10 x 41.3 ) / 1000

Voltdrop = 3.01 Volts

(Maximum permissible voltdrop (regulatuon - 525) = 11.5 Volts)

Calculated Cable size = 6 mm², Actual Earth conductor size = 2.5 mm²

Maximum Cable Length = 38.1 Metres

Kenny my friend, you will find that the manufacturer states 9.5KW at 240V and this equates to 8.7KW at 230v.

Therefore the Ib you refer to is 8725/230 = 37.93Amp
 
Hi Guys,

ive come across this same problem at least 3 times. All caused by 9.5kW showers on 6mm sq pvc/pvc.

The first two occasions, the problem lay in the 45Amp shower isolators, where the neutral conductor at the supply side, had melted the insulation completely, yet the conductor itself, remained intact.
Now the estimated lengths of these circuits(all separate addresses):

one 15m run, one 20m run (wired to 3036 30a fuse).

Now the third problem is the shower which is not yet turned on, as the plasterer has to finish, prior to commissioning of the circuit. The run is less than 5m and ive got the same problem, all for the sake of 1A.

Im going to comission the circuit, which is protected by a 40A breaker, housed with 30mA RCD (shower mcb unit) and ill monitor how it goes by checking the isolator, every so often. An l would suggest everyone else with this issue does the same.
 
i'd have liked kenny's post if i could reads it, but i've lost my magnifying glass. LOL.
 
Recommend upgrading to 10mm for sure, who knows what the cable is running through or under. In my opinion, if its borderline then it's wrong. No room for maybe's in this game..
 
I'm putting a new shower circuit in today. Here's how I ensure method C, by maintaining an air gap around the cable where it passes through the insulation layer.
This isn't finished yet. There's a Crabtree shower pull below that joist and there's another cable to put in yet.
I've left slack in the cable above the isolator just in case the cables should ever need reterminating. To reduce the chances of that happening the ends are treated with cord end ferrules which stop the strands spreading and improve the quality of the connection.
 

Attachments

  • tube.jpg
    317.8 KB · Views: 176
I'm putting a new shower circuit in today. Here's how I ensure method C, by maintaining an air gap around the cable where it passes through the insulation layer.
This isn't finished yet. There's a Crabtree shower pull below that joist and there's another cable to put in yet.
I've left slack in the cable above the isolator just in case the cables should ever need reterminating. To reduce the chances of that happening the ends are treated with cord end ferrules which stop the strands spreading and improve the quality of the connection.

Nice fabrication!
Well done!
 
Kenny my friend, you will find that the manufacturer states 9.5KW at 240V and this equates to 8.7KW at 230v.

Therefore the Ib you refer to is 8725/230 = 37.93Amp

At last! Someone else who undestands the shower ratings and the effects of Ohms Law when the voltage is reduced!

Except that I think you made an arithmetic error:

(9500 x 230) / 240 = 9100kW

Ib = 9500/240 = 39.6A
or
Ib = 9100/230 = 39.6A

So, fine on a 40A for non-continuous use (or leave a space on at least one side of the MCB)
 
Nice fabrication!
Well done!

Thanks. It takes less than 10 mins to cut that out of soil pipe and just a couple of minutes to install. There's a similar arrangement at the other two points the cables pass through the insulation. And the battons are simply screwed to the roof frame uprights.
This method also has the advantage of minimising the disturbance of the insulation and creating less 'fibre-gas'.
And, yes, it's a 9.5kW shower on a 40A MCB.
 
I understood that we had professional Electricians on this forum, who could at least use the Ohms Law!!!!

You have proved me wrong.

Here is my proof :-

Power=VxV/R

Rated power for the shower @ 240V is 9500W

R is the shower heater resistance

@ 240V, R = 240x240/9500W = 6.063 Ohms

Shower Ohms are constant at all volts, but the supply volts change to 230V

Power = VxV/R @ 230V =230x230/6.063 = 8725 Watts

Load Current @ 230V = Power/Volts = 8725/230 = 37.93Amps
 
Well spotted! I hadn't realised my quick calc was inaccurate. Should have been obvious though.


And as a double check that your calc is correct, I just got out my Triton catalogue and your answer agrees with their power equivalency table on the back page.

Thanks.
 
Looks good to me Moses, I've had no end of trouble in the past trying to explain exactly your conclusion. Not wishing to make things any more complicated that it needs to be but I have been finding very high supply voltages lately. I'm retired now but do small repair jobs for a charity and had to get Scottish Power in to reset to supply voltage. I found it was 251/2volts during the day and after they monitored it it was found to be 253/4 overnight. I recently checked my own house supply and found that it is up to 250/1. Do other people find this?? It makes any calculations extremely difficult. It does seem like an easy way of selling more KWh.
The increase in consumption is not linear but it is quite close to it in a domestic installation.
Philpot
 
Trouble is, whenever I test the actual voltage at a premises, it is always around 243v. Never come across a 230v supply yet. Now do the calcs :)
 
Last edited:
I'm putting a new shower circuit in today. Here's how I ensure method C, by maintaining an air gap around the cable where it passes through the insulation layer.
This isn't finished yet. There's a Crabtree shower pull below that joist and there's another cable to put in yet.
I've left slack in the cable above the isolator just in case the cables should ever need reterminating. To reduce the chances of that happening the ends are treated with cord end ferrules which stop the strands spreading and improve the quality of the connection.

You sure that your pipe is not considered "conduit". I always bring my oval conduit above the insulation but it is still "in conduit".
If someone can provide me with the area of air space around it that makes a cable "clipped direct" I would appreciate it. :)
 
Trouble is, whenever I test the actual voltage at a premises, it is always around 243v. Never come across a 230v supply yet. Now do the calcs :)
That doesn't matter.

We have to use 230V for calculations and this will ensure safety - all variations in the voltage must have been considered for the values.

If the manufacturer states 9.5kW @ 240V (39.58A) then you can convert this to 8.7kW @ 230V (37.82A) if you wish but not much point.
 
God, i used to just wire showers. Been in this business for 40 years so i must have killed hundreds and burnt down thousands of properties! Lol
 
only customer got no shower
so what would be your answer sedg?...sod it lets make sure the MCB dont let go and go for a 50A eh?....look sedgy, a 40A MCB to BSEN60898 aint gonna trip anyway for up to an hour with this load on it.....MCBs are there to PROTECT THE CABLE/INSTALL...so if it does let go its doing its job......
 
so what would be your answer sedg?...sod it lets make sure the MCB dont let go and go for a 50A eh?....look sedgy, a 40A MCB to BSEN60898 aint gonna trip anyway for up to an hour with this load on it.....MCBs are there to PROTECT THE CABLE/INSTALL...so if it does let go its doing its job......

Errr have I said something!!!
all I was saying last week is I recommend 10mm on a 40a so no iinconvenience occurs to the user
 
Recommend upgrading to 10mm for sure, who knows what the cable is running through or under. In my opinion, if its borderline then it's wrong. No room for maybe's in this game..

No such thing as border line in the regs. If it complies then its safe to do so. On a large job if you over specced everything that was borderline you would end up maybe 30% more than a comparison quote, both complying with regulations.
 
That doesn't matter.

We have to use 230V for calculations and this will ensure safety - all variations in the voltage must have been considered for the values.

If the manufacturer states 9.5kW @ 240V (39.58A) then you can convert this to 8.7kW @ 230V (37.82A) if you wish but not much point.

On the contrary, there is a very important point to be made here and all electricians must understand that while the nominal volts in UK are 230V, the actual volts are anywhere from 255V to 218V as already mentioned on in this thread.

For a 9500W shower for example, the currents are:
at 218V = 35.96A
at 230V = 37.93A
at 240V = 39.58A
at 252V = 41.56A

If you are consistently getting 252V at a property, and you install a 40A breaker for a 9.5Kw shower, then you will be called back to rectify the tripping shower, although you can try to explain to the customer as much as you like that the BRB states......, the nominal voltage is supposed to be ........ etc etc.
 
On the contrary, there is a very important point to be made here and all electricians must understand that while the nominal volts in UK are 230V, the actual volts are anywhere from 255V to 218V as already mentioned on in this thread.

For a 9500W shower for example, the currents are:
at 218V = 35.96A
at 230V = 37.93A
at 240V = 39.58A
at 252V = 41.56A

If you are consistently getting 252V at a property, and you install a 40A breaker for a 9.5Kw shower, then you will be called back to rectify the tripping shower, although you can try to explain to the customer as much as you like that the BRB states......, the nominal voltage is supposed to be ........ etc etc.

I doubt that very much, considering a typical shower will be only be anything from 10 to 20 minutes!! Maybe, just maybe, if you have a couple of pre-maddona teenage Princesses you could have a point!! lol!!
 
Last edited by a moderator:
I doubt that very much, considering a typical shower will be anything from 10 to 20 minutes!! Maybe, just maybe, if you have a couple of pre-maddona teenage Princesses you could have a point!! lol!!
cant see it letting go for the time it takes an avarage person to take a shower....but as you say...depends on what you call `avarage`...lol...
 
thing is...everyones talking about the MCB tripping.....the only way to eliminate this possibility is to upgrade the cable...and the MCB as appropriate...but i remember a thread in here about this subject a while ago....one of our regular posters said he`d clamped his shower at full pelt (9.5KW)....the result....about 35A....yet again we have manufacturers going over the top with the demand of their appliances.....same with cookers n all...
 

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
220
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock