Re: 95 mm 4 core cable, 30 m run, in ducting under buildings backed up by 200 amp fus

I don't believe at any point we were trying to calculate watts/meter. We were taking those as a given (H).

We are trying to calculate the heat disipated via the cable under varying conditions, so wee need to us Watts/m as a measure, and if you want to "FORGETN THE SOODING TABLES" you need IEC 60287.

You need to consider many factor's, from the construction of the cable, to the A/C resistance taking into account the Skin effect and the Proximety effect, then you need to consider the external influences, then as i have said after 4 pages of equations you can calculate the Heat disipation of the cable, the tables etc in BS 7671 are not far off the calculted.
 
Re: 95 mm 4 core cable, 30 m run, in ducting under buildings backed up by 200 amp fus

Yep, good idea, forget the soddin table altogether!!! lol!!
 
Re: 95 mm 4 core cable, 30 m run, in ducting under buildings backed up by 200 amp fus

I think there is confusion about the need to apply grouping factors to paralleled cables because different contributors have assumed the CSAs have been arrived at in different ways, and started with different tabulated CCCs...

Those saying no derating is needed, have assumed that a single cable of sufficient Iz with CSA Qmm² is split into n grouped parallel cables of Q/n mm². This gives equal CSA and greater heat dissipating area compared to the single cable, so no derating is needed. In fact the current density can be increased somewhat.
Example: Take one fully loaded 6.0mm², tabulated CCC 41A, and split it into four 1.5's. Current in each 1.5mmm² cable 41/4= 10.25A This is well within tabulated rating (17.5A) and even if Cg=0.65 is applied to the cables (11.375A) they are still good for more than 10.25A. So you don't need to consider the grouping factor separately.

Those saying that derating is needed, have assumed that n separate cables of Q/n mm² rated at their individual tabulated CCC have been paralleled up and grouped to form one circuit. Since the Iz for a cable of CSA Q/n is much more than 1/n x (Iz of cable CSA=Q) this would result in too high a current density, therefore derating is needed.
Example: Take four 1.5mm² cables tabulated at 17.5A CCC and parallel them up to get a cable totalling 6.0mm². You cannot work this at 4x 17.5 = 70A if the cables are grouped together. But if you apply the Cg of 0.65, you can work it at 70 x 0.65 = 45.5A.

So the disagreement is all in the choice of which CCC to start with. Use that of the individual cables and you'll need to derate. Use that of a cable equal to the combined CSA and you don't.
 
Last edited:
New posts

Reply to 95 mm 4 core cable, 30 m run, in ducting under buildings backed up by 200 amp fuses in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need to augment the underground supply to remote workshops at my own house. I’m struggling to understand the practical implications of voltage...
Replies
11
Views
2K
"Hello All", I am trying to find out some information to give to a Friend who is investigating the cause of Damp in his Home`s wall and has seen...
Replies
55
Views
11K
Geordie Spark
G
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock