Search for tools and product advice,

Discuss A good way to lower the grid voltage for economy purposes in the Electrical Engineering Chat area at ElectriciansForums.net

Reaction score
10
I have seen few cases where the owner of a factory uses transformer after the grid to lower the voltage, from 240 to 220v as a way to lower the consumption and at the end to save money.
I was wondering if an inverter will do much better the job instead of a simple transformer as you can keep or change the settings any time you would want to.
For example,one case is a 3phase 100Amps transformer and transform the voltage from 240v to 220v.If lets say in the future the factory expand his land to the next plot he will have a bigger voltage drop so he will have to raise the voltage to 230v so to meet the standards.He will need to change the transformer or remove it.
With an inverter it should be simpler just a different setting on the output voltage.
Any thoughts ?
 
Lowering the voltage does not in general save money. Heating loads go down but need to run longer. Modern lighting loads use switch mode techniques and are constant watts. Motor loads could stall but most likely draw more current to maintain torque.

The US uses half our voltage but their energy consumption is way above ours.
 
Agreed, and there have been discussions on and off in various forums - usually in relation to the DNOs doing it for short term demand management. Note that, as I read it, the customer savings they talk about are not through energy saving - but through deferring the need for network upgrades by managing peaks in demand.
There is no "magic box" that will cut power consumption - as suggested, if (eg) a certain amount of heat is needed, then lowering the voltage to a heater will simply result in that heater running running at a higher duty cycle.
However, if that heater is on full time AND whatever it is doing can be achieved with less heat, then adding a control to regulate the heater to provide what is needed and not a watt more will give a saving.
Similarly, quite a few motor driven things can be run more efficiently. For example, it's quite common to have DOL pumps where the flow rate is set by a throttling valve - inefficient by design, but cheap to implement (and most plumbers can understand the concept of a valve that's only part open to control the flow. Replacing these with an inverter driven pump, and setting the flow rate by setting the pump speed will also give a power saving - but costs for the inverter drive (and installation), and needs someone with more skills than most plumbers to set the drive correctly.
 
Yes , that it should be common sense. Nobody said is a free energy kind of thing.Is the Ohms Law.Lower the voltage lower the W lower the consumption.If the work needed is depend on exact energy for exact time it may not be useful for you as it will need more time to cover the exact energy needed so you draw the same amount of power without any "savings".
 

Reply to A good way to lower the grid voltage for economy purposes in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi. I am off grid, UK. There is no grid tie or connection and there is currently no potential for connection. Background: I use a Honda EU10i for...
Replies
0
Views
3K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
I
Has anyone had any experience with increased voltage levels caused by PV systems affecting any of the installed equipment on site? Had to reset an...
Replies
4
Views
2K
IronLiver
I
U
Hello! I’m after some advise/just to bounce ideas off and for someone to pick holes at my plan so I can address any issues at the early stages...
Replies
4
Views
2K
unclebob
U

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock