Is it acceptable to use a spare core in a 4 core armoured cable to carry 12volts DC when other cores in the same cable are carrying AC mains?
 
Read the regs! 528 (ish)

For a multicord cable... the cores of a band I circuit (eg 12v DC) should be separated by an earthed metal screen of equivalent current-carrying capacity to that of the largest core of a Band II circuit.

So, in a regular SWA cable, No.
 
As above, but it is permitted if the ELV is part of a control circuit for the LV, and the supplies are part of the same system. There are loads of SY and YY cables around that contain LV power and ELV control in the came cable. It's certainly not permitted to power a socket with some cores and 12V lighting with the others for example.
 
True. It's allowed in interlinked smoke alarm wiring. Line, neutral and (what is probably) an ELV connection as the interlink.

I'd worry too about the 0v reference for the 12v DC conductor. Is he thinking of using the mains earth:eek:
 
As long as every conductor is insulated to the highest voltage present i.e. 230 v then it is allowed to have a dc and ac voltage together
See below
 
Last edited:
Except where one of the following methods is adopted, neither a voltage Band I nor a voltage Band II circuit shall be contained in the same wiring system as a circuit of nominal voltage exceeding that of low voltage, and a Band I circuit shall not be contained in the same wiring system as a Band 2 circuit except where

  1. (i) Every cable or conductor is insulated for the highest voltage present
  2. (ii) Each conductor of a multicore cable is insulated for the highest voltage present in the cable
  3. (iii) The cables are insulated for their system voltage and installed in a separate compartment of a cable ducting or cable trunking system
  4. (iv) The cables are installed on a cable tray system where physical separation is provided by a partition
  5. (v) A separate conduit, trunking or ducting system is employed
  6. (vi) For a multicore cable, the cores of the Band I circuit are separated from the cores of the Band II circuit by an earthed metal screen of equivalent current-carrying capacity to that of the largest core of a Band II circuit
 
You will also have to take into account harmonic effects from the AC and quite possibly induced voltage on the DC circuit.
 
This is interesting as I come across this a lot and never use the cable for ELV as worry about interference.......so you reckon there can't be an induced voltage due to the insulation Ian? Surely that can't be the case as you can get induced voltage from LV to LV? Or am I getting it wrong? Would be handy to be able to use the same cable for ELV and LV.
 
How will you get induced voltage on the dc circuit if the cores are insulated to the highest voltage present i.e. 230volts?

Insulation rating does not effect induction, however as the OP is discussing a multicore cable then to comply like you and others have put it has to have a earthed screening which will block any chance of an induced current between the 2 categories as we must assume AC mains means 230/400 volt ac against his 12v DC, as for harmonics, if you suspect this as an issue then the wiring and preventative measures in total needs careful design.
 
Insulation rating does not effect induction, however as the OP is discussing a multicore cable then to comply like you and others have put it has to have a earthed screening which will block any chance of an induced current between the 2 categories as we must assume AC mains means 230/400 volt ac against his 12v DC, as for harmonics, if you suspect this as an issue then the wiring and preventative measures in total needs careful design.
Band 1 (ELV) and Band 11 (LV) circuits can be contained in the same cable where each conductor of a multicore cable is insulated to the highest voltage present i.e the Band 11 voltage
alternatively this is allowed where the cores of the Band 1 circuit are seperated by an earthed metal screen of equivelant current-carrying capacity to that of the largest core of the Band 11 circuit
As stated in option 2 I listed given in bs 7671
It's how I interpreted it
 
Band 1 (ELV) and Band 11 (LV) circuits can be contained in the same cable where each conductor of a multicore cable is insulated to the highest voltage present i.e the Band 11 voltage
As stated in option 2 given in bs 7671

As I interpret it that is for the same wiring system, they have made a specific regulation exemption No' 6 for multicore cable as that does not fall under the term same wiring system due to the fact its a cable and not multiple cables or cores in a wiring system.
 
I deal a lot with mixed cable voltages and induction is a big issue in my job, also there is the concern of a damage cable raising the voltage on the ELV side to LV levels which can be a fire risk if not a life risk... cables damage can be common and point 6 notes a earthed screening for this purpose in multicore cable otherwies why write it into the regs to start with as we have other regulations to deal with interference between cables.
 
As I interpret it that is for the same wiring system, they have made a specific regulation exemption No' 6 for multicore cable as that does not fall under the term same wiring system due to the fact its a cable and not multiple cables or cores in a wiring system.
yep agreed I've re read it over and it does say system , I even wrote the dam thing on the thread.
 
This is interesting as I come across this a lot and never use the cable for ELV as worry about interference.......so you reckon there can't be an induced voltage due to the insulation Ian? Surely that can't be the case as you can get induced voltage from LV to LV? Or am I getting it wrong? Would be handy to be able to use the same cable for ELV and LV.
See further replies in the thread pal.
As Darkwood pointed out,
If the same cable used for containing both bands it needs to be as option 6 and have an earthed screen
 

Reply to AC mains and low voltage DC in same cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
905
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
571
I used 12v dc from a 13 plate car battery to power a 12v dianamo dc motor and brought in an alternator to change the battery using the rotation of...
Replies
7
Views
706
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
633
Im just curious as to peoples thoughts on the following install I seen on a video from an Electrical firm today and they did the following: Ran...
Replies
2
Views
539

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock