this farm shop you saying ,calculate the existing load before the extra load .
you need to put some pics on here to so we can see the existing supply.
candy man !

Calculate? What on earth would you want to do that for?
Just pick an MCB rating that sounds good and add a generous quantity of RCDs 'just in case'
 
Sounds if you pulled a 16mm cpc in with the sub then this would get you too your max zs value. Is this doable? Stay away from rcds & mcbs on large subs if possible for discrimination of ocpd in series during fault condition. Even if you end up TT the barn the sub would still need to meet TN disconnection times up to the isolator. Understand your in a pickle but dont get led by the customers "tight budge" as you will still need to cert your work.
 
It's a 16mm 4 core armoured. Not much volt drop at all. It's about 30 meters but that's just from r1 and rn test and rough distance

Not much at all? That's a great answer to a technical question.

A quick smoke packet calculation based on the full ratings of the ocpds suggests that your looking at 4.5V drop on the 63A submain and 3V drop on the 50A submain after that, giving a total of 7.5V drop on the submains alone.
That leaves you very little left for your final power circuits and nothing at all for any final lighting circuits.
 
Make sure that RCD up front (100ma) is time delayed, if you install a 30ma rcd down stream the 100ma rcd could still trip unless time delayed.
 

Reply to Adding sub board to main consumer unit on tt in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
827
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
761
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
494
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock