Search the forum,

Discuss Addressable fire systems in the UK Electrical Forum area at ElectriciansForums.net

TheCodboy

-
Arms
Reaction score
109
Hi all, I'm looking for some help & advice understanding addressable fire systems. I'm helping a small team out pulling in enhanced FP for a fire install. I've done a little bit of addressable fire stuff before, but not much. I'm just looking for info with regards to Interfaces, power supplies for VAD's etc. Obviously I'm trying to pick as much up as I go, but we all know what its like sometimes when everyone is really busy/stressed on site! Any help and info would be much appreciated!
 
Designing the systems in an art in itself, and I'm about 5 years out of date now, but basically the loop card will have a max current, and the devices on the loop cannot exceed this. You want a couple of loop isolators on the loop, and some devices have this feature built in.
When fitting sounder bases don't connect the sounder part initially, so you can IR test the loop when it's complete. Manual call points have a little link device for this purpose.
There are IO units which sit on the loop that provide volt free relay outputs and resistor based fault tolerant inputs.

You can autolearn the loop on an Advanced panel without laptop and software, but it's handy to have these.

There's a free tool to calculate loop loadings for XP95 protocol from Apollo here:

Hope that helps a bit. Advanced is a very forgiving first one to do so I'm sure you'll sort it out!
 
Designing the systems in an art in itself, and I'm about 5 years out of date now, but basically the loop card will have a max current, and the devices on the loop cannot exceed this. You want a couple of loop isolators on the loop, and some devices have this feature built in.
When fitting sounder bases don't connect the sounder part initially, so you can IR test the loop when it's complete. Manual call points have a little link device for this purpose.
There are IO units which sit on the loop that provide volt free relay outputs and resistor based fault tolerant inputs.

You can autolearn the loop on an Advanced panel without laptop and software, but it's handy to have these.

There's a free tool to calculate loop loadings for XP95 protocol from Apollo here:

Hope that helps a bit. Advanced is a very forgiving first one to do so I'm sure you'll sort it out!
It's a big job and it's all designed. I'm just pulling cable in to the drawings. I just want to get a better understanding of how it all works. I've got a very basic understanding,but that's about it. I've got an old Advanced Mx panel in the loft and I've just bought some second hand Apollo XP95 kit off eBay (bases,smokes,VADS,I/O,MCP's) so I'm gonna try building a rig. There just doesn't seem to be much information online/YouTube etc like there is for electrical learners etc.
 
PXL_20220123_185709846.MP~2.jpg
PXL_20220123_185700074~2.jpg
PXL_20220123_185750387~2.jpg
 

Reply to Addressable fire systems in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock