Discuss Advice on generator earthing in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
92
Hi, I am looking for some advice.

I have been asked to quote for an installation where a generator will be used to supply occasional power to an installation that is not connected to the grid.
The IET says a floating earth generator needs to be modified to connect earth and neutral if more than one item of class 1 equipment may be connected. That is not practical as the installation will probably be in use long after the generator is changed, so the earth to neutral connection needs to happen in the installation to accommodate changing generators.
My current plan is to have a 16A CEEForm inlet to the fixed installation with the neutral earth link in the CEEform inlet, but there are two ways to provide the earth neutral link.

  1. Take the earth for the installation and connect it to the neutral and earth from the generator.
  2. Take the earth for the installation and connect it to the neutral from the generator only.
Option 1 means that all the earth is connected to neutral from the generator through the entire installation.
Option 2 will leave the earth between the generator and CEEform inlet as supplied by the generator, and the earth from the inlet onwards with earth connected to neutral.

There is also the option of leaving the connecting of earth and neutral until the small consumer unit, but I believe the sooner the better for this link. Am I correct?

Regards
 
Hi

What type of installation is it?

Cheers


Hi,

It’s a farm building, demolished and a rebuilt on the same footprint as a wooden insulated structure that is intended to be used a communal area for youth camps.
It has a larger meeting area and two rooms with bunk beds for up to 8 leaders.
The building is over 500 meters from the nearest electrical supply, so they want to have a generator providing a small amount of power (probably 1Kw) for recharging phones, laptops etc. for when the building is in use. No kettles or anything requiring that sort of power according to the customer.
Lighting has been requested as LED, and as 12V LED strip will run directly off a 12V car battery, I have suggested they use a couple of solar panels they already have but are not using to recharge the car battery leaving the lighting system a completely independent 12V system with no connection to the generator output.

I hope this helps

Thanks
 
Depending on how often it's used, they might be best charging phones off the battery via the usual 12V to 5V USB car chargers plus maybe a low power inverter for laptop chargers. Then they won't have to have the generator running all night just for a small charging load. Could perhaps use the generator as a backup charger for the battery in case of extended periods without sun. Many small generators have a 12V output for battery charging.
 
What type of generator are they planning on using? The poor thing probably won't like all that electronic loading without a bit of resistive load to ballast it.
 
What type of generator are they planning on using? The poor thing probably won't like all that electronic loading without a bit of resistive load to ballast it.

Interesting. I have not considered the type of loading. Do you have any suggestions for a suitable resistive load?
I have assumed the generator purchased would have enough headroom for it not to be a worry. Would that bypass th issue?

The client has not spoken about the actual generator. I have suggested they consider an inverter by preference, or an AVR generator as a minimum specification. I would hate to think what a fake apple charger would do with an unregulated slightly unstable power supply.
 
Interesting. I have not considered the type of loading. Do you have any suggestions for a suitable resistive load?
I have assumed the generator purchased would have enough headroom for it not to be a worry. Would that bypass th issue?

The client has not spoken about the actual generator. I have suggested they consider an inverter by preference, or an AVR generator as a minimum specification. I would hate to think what a fake apple charger would do with an unregulated slightly unstable power supply.

If you aren't supplying the generator or advising on the type to get then don't worry about it, but then you also cannot know what to do with the earthing arrangements can you?

A genuine apple charger probably won't fare much better than the fake one.
 
If you aren't supplying the generator or advising on the type to get then don't worry about it, but then you also cannot know what to do with the earthing arrangements can you?

You can set up the earthing so it does not matter what type of earthing the generator has, the RCD downstream will work. You can even set it up so a floating earth generator will still be floating up to the start of the fixed installation, then you connect neutral and fixed installation earth creating a TN-C-S System.
 
You can set up the earthing so it does not matter what type of earthing the generator has, the RCD downstream will work. You can even set it up so a floating earth generator will still be floating up to the start of the fixed installation, then you connect neutral and fixed installation earth creating a TN-C-S System.

It does matter what type of earthing the generator has! If someone connects a generator with an earthed centre tapped output to it or if they connect a generator with an internal N-E link then you have a problem.
 
It does matter what type of earthing the generator has! If someone connects a generator with an earthed centre tapped output to it or if they connect a generator with an internal N-E link then you have a problem.

Sorry, I do not know what a “earthed centre tapped output” is, however I still struggle to understand how this will affect the installation as the generator earthing stops at the Ceeform connector into the installation, and from there, it is only the live and neutral of the generator that continue into the installation, the neutral being split to provide an earth before the consumer unit.
 
The whole point of this exercise, is to provide an earth for the generator.
If the generator already has an earth, then you don't need to provide one.
Hence my earlier post, that option1 is pointless.
 
The whole point of this exercise, is to provide an earth for the generator.
If the generator already has an earth, then you don't need to provide one.
Hence my earlier post, that option1 is pointless.

I agree, the more the discussion goes on the more it appears option 2 is the only way forward, especially as it now appears option 1 may cause significant problems to some design of generator.

I am always keen to understand fully and learn from more experienced electricians. I hope to understand the problem Davesparks sees with generator earthing.
 
Sorry, I do not know what a “earthed centre tapped output” is, however I still struggle to understand how this will affect the installation as the generator earthing stops at the Ceeform connector into the installation, and from there, it is only the live and neutral of the generator that continue into the installation, the neutral being split to provide an earth before the consumer unit.

Actually, thinking about “earthed centre tapped output” this morning (a slow week for work) I suspect this may be what I have read about known as “V-O-V” generators, and those should not be used for domestic standby or similar installations. My understanding is that in V-O-V generators, the neutral actually has potential, and is NOT tied to 0v like a normal star point. If that is the case, then regular RCD’s will not work and the installation will not be suitably protected.
I would think an inverter generator will not have this output configuration, but I do not know if AVR output generators may still be V-O-V. I believe the clients need to confirm in writing that the wiring of the generator they buy is not a V-O-V configuration before purchase.
 

Reply to Advice on generator earthing in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
280
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
444
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock