Discuss Advice on work I've had done in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hello,

I've recently had some outside lights fitted, there is about 10 of them, all LED. The electricans took the cable from the fuse board down into my basement void where other services are running and then out to the garden. Outside they have used armoured cable, 1.5mm, about 20-30meters in total I'd have thought. But in the basement void, it's about another 20m from the fuseboard end to the outside but they have used a 0.75mm 3 core white flex cable.

The circuit breaker is 6 amps.

I don't know whether that is good or bad but to me something isn't quite sitting right having a cable half the size of the armoured cable, it looks like they've used a cable very similar to the flex hanging down on my pendants for 20m.

Should I be concerned or is it ok? Since I have had the work done I've been hearing bad things about the company I used so I was hoping someone on here could give me some advice.

Thank you.
 
Have you paid in full for this work?
Did you receive and paperwork (electrical certs) for this work?
What wattage lights are fitted?

Oh... I keep forgetting....
Welcome to the forum mate.
 
Hello,

I've recently had some outside lights fitted, there is about 10 of them, all LED. The electricans took the cable from the fuse board down into my basement void where other services are running and then out to the garden. Outside they have used armoured cable, 1.5mm, about 20-30meters in total I'd have thought. But in the basement void, it's about another 20m from the fuseboard end to the outside but they have used a 0.75mm 3 core white flex cable.

The circuit breaker is 6 amps.

I don't know whether that is good or bad but to me something isn't quite sitting right having a cable half the size of the armoured cable, it looks like they've used a cable very similar to the flex hanging down on my pendants for 20m.

Should I be concerned or is it ok? Since I have had the work done I've been hearing bad things about the company I used so I was hoping someone on here could give me some advice.

Thank you.
Welcome
 
Have you paid in full for this work?
Did you receive and paperwork (electrical certs) for this work?
What wattage lights are fitted?

Oh... I keep forgetting....
Welcome to the forum mate.

Thanks for the reply!

Yes I have paid for the work but I was never given any paperwork from them.

The lights I think are 3.5 watt.
 
Thanks for the reply!

Yes I have paid for the work but I was never given any paperwork from them.

The lights I think are 3.5 watt.

So you have about 35W in total. About 0.2A
1.5mm SWA cable is the smallest size you can get.
0.75mm 3 core white flex is rated for 6A.
Only think that might be an issue is volt drop but at less than 0.2A load then there shouldn't be a problem.

If this circuit for the 10 LED lights a new circuit? (is the 6A breaker new) or is it an existing breaker for the lights?
 
Have you raised your concerns with the person(s) that did the work?

I have tried to contact them but he wont pick up his phone or reply to my email.


So you have about 35W in total. About 0.2A
1.5mm SWA cable is the smallest size you can get.
0.75mm 3 core white flex is rated for 6A.
Only think that might be an issue is volt drop but at less than 0.2A load then there shouldn't be a problem.

If this circuit for the 10 LED lights a new circuit? (is the 6A breaker new) or is it an existing breaker for the lights?

Yes it's a new circuit, the house was re-wired maybe about 10 years ago and the fuse board had about 3 spare gaps in it with some plastic covers where the circuit breakers would be so I assume it's a new 6A one.

One of the reasons I was concerned, other than the fact it was half the size of armoured cable is because from what I have seen online it's not good practice to wire in a flex cable or that it should be fused down to 3A? I found it a confusing to be honest so I've probably got it completely wrong...
 
Also, as @peterhyper
I have tried to contact them but he wont pick up his phone or reply to my email.




Yes it's a new circuit, the house was re-wired maybe about 10 years ago and the fuse board had about 3 spare gaps in it with some plastic covers where the circuit breakers would be so I assume it's a new 6A one.

One of the reasons I was concerned, other than the fact it was half the size of armoured cable is because from what I have seen online it's not good practice to wire in a flex cable or that it should be fused down to 3A? I found it a confusing to be honest so I've probably got it completely wrong...

Ok, so it's a new circuit. Depending on where you are in the UK, this falls under Part P and the work needs to be notified to your Local Building Control Body.
Yes flex is not ideal for this circuit, but it's not 'unsafe'. 99% of electricians would not have used flex.
With a new circuit you should have received an Electrical Installation Certificate.
 
Last edited:
Hello,

I've recently had some outside lights fitted, there is about 10 of them, all LED. The electricans took the cable from the fuse board down into my basement void where other services are running and then out to the garden. Outside they have used armoured cable, 1.5mm, about 20-30meters in total I'd have thought. But in the basement void, it's about another 20m from the fuseboard end to the outside but they have used a 0.75mm 3 core white flex cable.

The circuit breaker is 6 amps.

I don't know whether that is good or bad but to me something isn't quite sitting right having a cable half the size of the armoured cable, it looks like they've used a cable very similar to the flex hanging down on my pendants for 20m.

Should I be concerned or is it ok? Since I have had the work done I've been hearing bad things about the company I used so I was hoping someone on here could give me some advice.

Thank you.
Where are you situated, could come and give you an opinion if it's not to far from Northampton
 
New posts

Reply to Advice on work I've had done in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
772
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
686
I have a Security Light on my patio and until recently it worked fine. It stopped working and I couldn't decide if it was the LED Floodlight or...
Replies
6
Views
508
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
688

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock