Discuss Advice ref blinking lights all circuits in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi there,


I should start by saying I am not an electrician, but am after some advice as we have a problem that we aren’t getting any answers on.

In January, we had a new fuse board installed to replace an old edition one. This is a recent Wylex model with circuit breakers. The electricians who installed it also added some outdoor lights, a couple of sockets in the kitchen and updated a few sockets around the house for us.

Approx 10 days after the work completed we began to notice intermittent blinking on lights across both upstairs and downstairs lights and on lamps plugged into sockets. There is no rhyme nor reason to the blink – it doesn’t matter if any appliances are running or none, so we’ve ruled out a surge due to boiler, fridge, etc.

We spoke with the electrician who did the work, they inspected the connections at the board and said everything looked fine and they suggested it was likely to be a supply issue. Powergrid came out, inspected and setup voltage recording device and left that running for about 8 days. They say that there is no fluctuations from their side that would cause “flicker” so have said it’s not an issue from their end.

I’ve spoken with the electricians who did the install again, but they seem void of any idea on what to look for or what could be causing this problem.

Does anyone on this forum have experience of similar issues being related to anything non-supply related – so from the board onward internally? Is it possible a fault could be present on the board itself?

From searching google, there’s lots of suggestions that flicker on all circuits including sockets is likely to be a supply issue, but this isn’t really what I’d call a flicker. It’s a very short blink. More noticeable on filament bulbs than the LED types. Not ever so frequent enough to cause headaches or anything, but frustrating, annoying and worrying as I have 2 young kids and I am really paranoid about electrical safety (which is kind of the reason we had the old fuseboard replaced in the first place!).

Thanks in advance for any advice or ideas offered.
 
It could be the main switch is not connected to the busbar properly and when there is load on the board it is making the circuits flash, get the sparks back to treble check all connections. If they refuse to do so, get a spark in to sort it, get his report and send the company the invoice.
 
a favourite is the busbar incorrectly fitted to 1 or more MCBs. if you are competent to do this safely, with the board turned OFF at main switch , pull off the busbar cover and use a mirror if necessary to see if the busbar is behind the cage clamp. Remember to replace busbar cover before swiychting back on. DO NOT ATTEMPT UNLESS COMPETENT TO DO SO.
 
Hi there,


I should start by saying I am not an electrician, but am after some advice as we have a problem that we aren’t getting any answers on.

In January, we had a new fuse board installed to replace an old edition one. This is a recent Wylex model with circuit breakers. The electricians who installed it also added some outdoor lights, a couple of sockets in the kitchen and updated a few sockets around the house for us.

Approx 10 days after the work completed we began to notice intermittent blinking on lights across both upstairs and downstairs lights and on lamps plugged into sockets. There is no rhyme nor reason to the blink – it doesn’t matter if any appliances are running or none, so we’ve ruled out a surge due to boiler, fridge, etc.

We spoke with the electrician who did the work, they inspected the connections at the board and said everything looked fine and they suggested it was likely to be a supply issue. Powergrid came out, inspected and setup voltage recording device and left that running for about 8 days. They say that there is no fluctuations from their side that would cause “flicker” so have said it’s not an issue from their end.

I’ve spoken with the electricians who did the install again, but they seem void of any idea on what to look for or what could be causing this problem.

Does anyone on this forum have experience of similar issues being related to anything non-supply related – so from the board onward internally? Is it possible a fault could be present on the board itself?

From searching google, there’s lots of suggestions that flicker on all circuits including sockets is likely to be a supply issue, but this isn’t really what I’d call a flicker. It’s a very short blink. More noticeable on filament bulbs than the LED types. Not ever so frequent enough to cause headaches or anything, but frustrating, annoying and worrying as I have 2 young kids and I am really paranoid about electrical safety (which is kind of the reason we had the old fuseboard replaced in the first place!).

Thanks in advance for any advice or ideas offered.
Sorry to hear about your problems Luke, did you have these flickering problems before you had your CU changed? When you called the Electricians back due to the problem, you say they looked at the connections in the CU and all looked OK, but did they actually check the soundness. tightness of all the connections? it's all very well them saying it looks OK but that's not the answer, checking the integrety of the connections would be the best option,
does the flicker occur randomly, is there any vibrations that may cause a loose connection to make and break, you say you have a couple kids, and we all know what they are like slamming doors etc.
Maybe one of the Forum Members close to your location, could offer to come and take a look, you're a bit to far away for me to offer, hope you get it sorted.
One more thing did the Electricians leave any certificates/paperwork with you when they left? you should have been in receipt of an Electrical Installation Certificate (EIR) on completion of the works.
 
Would really p*** me off if there were no issues before work was done and after so called ‘professional’ had conducted work that resulted in an issue, that ‘professional’ showed little interest in getting it fixed. You sure they were competent to do the work in the first place?
 
Hi, thanks for the reply.

Yes, they checked the tightness of everything and I stood over them while they did it. In fairness, they've been very good, but seem stumped as to what the issue can be.

Yes, we have received the EIR paperwork and certificates.

This wasn't happening prior to the work being carried out, which is why I am making that link.

I also know for a fact that we didn't notice it in the immediate few days after the installation either - it was approx 9-10 days after that we begun to notice it.

The flicker is random - no vibrations - happens in all rooms at all different times of the day, even when kids are asleep.

It is really weird - there is no logical starting point to look for a fault as it is displaying on the upstairs lighting circuit, the downstairs lighting and also across table lamps plugged into sockets both upstairs and downstairs.

The one other thing that they did change was a previous shared neutral on the landing - they made use of a redundant cable that used to run to an old whirlpool bath pump that is was no longer in use to provide a neutral to the upstairs hall light. I have wondered if that could be a root cause, but then not sure why that would affect the sockets as well.
 
If you have any high load apliences sutch as a shower or oven, or an electric heater, try switching these on and off and see if it affects the lights. A very slight dimming is normal but if its quite significant that could indicate a poor connection.

If you can get the electricians back, try and persuade them to remove and reterminate all the connections, including re fitting the busbars and neutral links to RCDs etc, and check both sides of the main switch. Any poor connections may become obvoius then, as if they have been arcing there will be some carbon buildup at the connections.

It could also be the connection of the meter tails into the meter that have worked loose if they were disturbed when the new board was fitted.

If you/they can get access to an IR camera this could help trace any high resistance connections whilst everything is switched on.
 
Hi, thanks for the reply.

Yes, they checked the tightness of everything and I stood over them while they did it. In fairness, they've been very good, but seem stumped as to what the issue can be.

Yes, we have received the EIR paperwork and certificates.

This wasn't happening prior to the work being carried out, which is why I am making that link.

I also know for a fact that we didn't notice it in the immediate few days after the installation either - it was approx 9-10 days after that we begun to notice it.

The flicker is random - no vibrations - happens in all rooms at all different times of the day, even when kids are asleep.

It is really weird - there is no logical starting point to look for a fault as it is displaying on the upstairs lighting circuit, the downstairs lighting and also across table lamps plugged into sockets both upstairs and downstairs.

The one other thing that they did change was a previous shared neutral on the landing - they made use of a redundant cable that used to run to an old whirlpool bath pump that is was no longer in use to provide a neutral to the upstairs hall light. I have wondered if that could be a root cause, but then not sure why that would affect the sockets as well.
Bit naughty that last bit Luke, sounds like they had some RCD tripping problems and took the roughest route out of the problem, not something I would do, neither I suspect would anyone else, could be wrong of course.
 
Thanks for all the replies everyone - really appreciate it.

I've just called to arrange a return visit from the electricians for a couple of weeks time - they are going to check all the connections and busbars again and also investigate the neutral that they took that existing cable for - they have even suggested putting that back as it was to see if it stops the issue. Not sure if that would be the cause though as it's happening on the sockets too.

@shaun1 - There doesn't seem to be any impact to the lighting when we put the oven on. The shower is a thermostatic valve mains pressured so that wouldn't give an indication. We have an electric fire that we don't really make much use of - I will try that this evening to see if that has any impact.
 
Bit naughty that last bit Luke, sounds like they had some RCD tripping problems and took the roughest route out of the problem, not something I would do, neither I suspect would anyone else, could be wrong of course.

Indeed they had RCD tripping issues. They returned the following day with the intention of running a new cable from the board under the stairs up to the attic space above the light in the hallway. When they were seeking the easiest route to run the cable, they found the old cable that had been disconnected from the old bath pump and suggested using that as it was already there and would be less disruptive. I agreed because it made sense. Like I said above though, I am not sure if that would cause all the circuits to display these blinks?

Another point to add - we aren't experiencing any other issues with anything plugged into the sockets - TV's, chargers, radio, kettle, large appliances, etc - all running as normal.
 
Indeed they had RCD tripping issues. They returned the following day with the intention of running a new cable from the board under the stairs up to the attic space above the light in the hallway. When they were seeking the easiest route to run the cable, they found the old cable that had been disconnected from the old bath pump and suggested using that as it was already there and would be less disruptive. I agreed because it made sense. Like I said above though, I am not sure if that would cause all the circuits to display these blinks?

Another point to add - we aren't experiencing any other issues with anything plugged into the sockets - TV's, chargers, radio, kettle, large appliances, etc - all running as normal.
Thanks for the update
 
Indeed they had RCD tripping issues. They returned the following day with the intention of running a new cable from the board under the stairs up to the attic space above the light in the hallway. When they were seeking the easiest route to run the cable, they found the old cable that had been disconnected from the old bath pump and suggested using that as it was already there and would be less disruptive. I agreed because it made sense. Like I said above though, I am not sure if that would cause all the circuits to display these blinks?

Another point to add - we aren't experiencing any other issues with anything plugged into the sockets - TV's, chargers, radio, kettle, large appliances, etc - all running as normal.

Hi,this would cause me to wonder,if they did adequate testing,prior to the fitting of the new DB,and,afterwards.

A few days later,is not the time this issue should have come to light.

Are the lighting circuits fed from one or two MCB's?
Where did the feeds originate from,for the outside lights?
Have the MCB's been removed and inspected,or just tightened?
 
Hi,this would cause me to wonder,if they did adequate testing,prior to the fitting of the new DB,and,afterwards.

A few days later,is not the time this issue should have come to light.
Reckon you are spot on there PEG they must have had a tripping RCD problem, typical borrowed N on the two lighting circuits= no initial testing, connect up, conduct bang test etc.
Are the lighting circuits fed from one or two MCB's?
Where did the feeds originate from,for the outside lights?
Have the MCB's been removed and inspected,or just tightened?
 
Hi,this would cause me to wonder,if they did adequate testing,prior to the fitting of the new DB,and,afterwards.

A few days later,is not the time this issue should have come to light.

Are the lighting circuits fed from one or two MCB's?
Where did the feeds originate from,for the outside lights?
Have the MCB's been removed and inspected,or just tightened?

Hi, thanks for the reply.

They are fed from 2 MCBs. One for upstairs and one for downstairs. As I understood it (I was at work while the work took place, my wife was home), when they connected it all up the lights kept tripping upstairs - so the options we were given were to leave the borrowed neutral as it was and only have them on a single MCB or to connect a new neutral to the board and the light - which is how we got to the scenario mentioned above where they utilised the existing disconnected cable.

The feeds from the outside lights - no idea on that. They are on a separate switch on the board (not sure if that indicates where they originate?) excuse my ignorance on this - I'm not electrically minded :)

The MCB's have not been removed and inspected - it was just a tightening that was performed.
 
using an old cable is a bit risky especially if it went to a pool /hot tub?
unless they did an I.R. test on it to prove it was serviceable,
it may have had a little moisture in it. but as others have suggested this sounds like a loose connection somewhere.
also loose neutrals or intermittent neutral faults can cause electronics to mysteriously fail.
 
Thanks for all the responses so far.

One question I have is around the safety of using the electrics while this is going on. The electricians have said they cannot come back to do a proper inspection until after Easter, and I've booked them in for the Thursday of that week - so, 3 weeks tomorrow.

Are we safe to continue using the lights and sockets as we have been doing? If the fault is caused by a loose connection in the panel somewhere - should the breakers work to cut the supply if the fault developed into something more significant?

Thanks!
 
Thanks for all the responses so far.

One question I have is around the safety of using the electrics while this is going on. The electricians have said they cannot come back to do a proper inspection until after Easter, and I've booked them in for the Thursday of that week - so, 3 weeks tomorrow.

Are we safe to continue using the lights and sockets as we have been doing? If the fault is caused by a loose connection in the panel somewhere - should the breakers work to cut the supply if the fault developed into something more significant?

Thanks!
Can't come back for 3 weeks, to what could be a dangerous installation? am I smelling a rat or just being a misery, speak to them again and insist that the response is sooner rather than later and if they still play hardball get someone else in and charge the original Electrician, could be rather tricky, but safer in my book, 3 weeks my derriere.
 
Last edited:
Can't come back for 3 weeks, to what could be a dangerous installation? am I smelling a rat or just being a misery, speak to them again and insist that the response is sooner rather than later and if they still play hardball get someone else in and charge the original Electrician, could be rather tricky, but safer in my book, 3 weeks my derriere.

I've spoken with them again and managed to get them to agree to return next Thursday. I don't want to speak ill of them - they have done work for us previously at a property we lived at before and that went well - in fact a similar job to this one with a fuse board swap out. We were also pleased with the work they did for us on this job as well - it's only since this blinking started that I'm left scratching my head looking for answers.

I don't understand how the shared neutral swap out for the hallway and landing lights could cause a knock on effect to the rest of the circuits and lamps on the sockets though.

I am a completely ignorant with how electrics work, but from what I've seen online and from speaking with people, the suggestion appears to be the issue is either in the box or via supply - this based on the fact that the lamps are also producing the same blink.

One other thing - it's not really noticeable on LED candle bulbs, but is on spot lights (LED and halogen) and oldschool fillament / energy bulbs. Any idea why this would be?

Does anyone actually have previous experience of similar symptoms that were resolved via a particular course of action? It seems very much shooting in the dark to locate the source of the problem.
 
I've spoken with them again and managed to get them to agree to return next Thursday. I don't want to speak ill of them - they have done work for us previously at a property we lived at before and that went well - in fact a similar job to this one with a fuse board swap out. We were also pleased with the work they did for us on this job as well - it's only since this blinking started that I'm left scratching my head looking for answers.

I don't understand how the shared neutral swap out for the hallway and landing lights could cause a knock on effect to the rest of the circuits and lamps on the sockets though.

I am a completely ignorant with how electrics work, but from what I've seen online and from speaking with people, the suggestion appears to be the issue is either in the box or via supply - this based on the fact that the lamps are also producing the same blink.

One other thing - it's not really noticeable on LED candle bulbs, but is on spot lights (LED and halogen) and oldschool fillament / energy bulbs. Any idea why this would be?

Does anyone actually have previous experience of similar symptoms that were resolved via a particular course of action? It seems very much shooting in the dark to locate the source of the problem.
Personalyi think the shared N maybe a red herring, it may not be the reason for the blinkung light issue, my problem withe the issue is, they should have checked this issue prior to the CU fitout, it's not an ideal method to use a cable that has been redundant to solve a problem that should have been sorted earlier, I would go as far as saying it's a rough solution, but without seeing the install it's maybe jumping the gun.
 

Reply to Advice ref blinking lights all circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
630
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
646
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
720
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
899

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock