, it's not an ideal method to use a cable that has been redundant to solve a problem that should have been sorted earlier, I would go as far as saying it's a rough solution, but without seeing the install it's maybe jumping the gun.
I don't necessarily agree there, Pete. If they've tested the cable and it's in decent nick, it could well have saved a lot of trouble both for them and Luke. It's not a full rewire, after all. Maybe they should have taken into account the shared neutral, but they obviously got to the bottom of that problem, quite easily. As you say, it's easy to assume without seeing. They seem a decent crew.
 
I’m far from being an expert but logically if you’ve had the CU replaced on a system that was ok before and have a flicker on two seperate circuits it suggests the fault is upstream from the MCB’s. As others have suggested ... loose connections to mainswitch, tails etc. Presumably there’s some RCDs in there as well?
 
I would normally say that it may be a supply fault on one of the phases. Same thing happened in my house with blinking lights.
I didn’t ask around the neighbours to see if the same was happening next door or 2 down or 3 down to correspond with the phase (although the OP could do this if not done already)
The supplier corrected a fault on the supply and has been good since.
The OP had the DNO out to data log so that would and should have picked up something supply side.
I’m with everyone else otherwise and root for something loose that needs a wiggle to check.
Hope you get sorted.
 
I'm going to stick my neck out and say an intermittent neutral joint in the cable under the pavement, where the house is tapped off the main feed.
I want a prize if I'm right though.
 
One other thing - it's not really noticeable on LED candle bulbs, but is on spot lights (LED and halogen) and oldschool fillament / energy bulbs. Any idea why this would be?

Tungsten filament bulbs are very basic - the filament is connected between live and neutral and the light output is (kind-of) proportional to the voltage across it. So when there is a dip you will see a drop in brightness.

LED bulbs and most electronics are powered via electronic outputs, which can adjust themselves so they always give the same output for a wide range of input voltages right down to 100v (we are at 230v (which is usually 240) here in the uk). They also have capacitors which act like a battery to store current and smooth the output during voltage fluctuations.

With regards to safety, loose connections and high resistance connections create localised heating, which can then make the problem worse, and can eventually become a fire risk. Circuit breakers and RCDs may not operate in this situation as there is no overcurrent or imbalance.

There has just been an amendment to the regulations stipulating that consumer units in houses now have to be made from a non combustible material to contain faults such as this and to prevent fires.

Whilst I don't think you need to immediately panic if there's no obvious cause, I don't think waiting weeks is acceptable. If the flickering gets worse or more often, or you notice a burning or fishy smell (melting insulation) around the CU then it may be time to turn of and demand they come back immediately.
 
Had something similar once.
Turned out to be an ill fitting main fuse holder.
The sprung legs were corroded and had lost tension over the years. Also the screw terminals for all conductors at the head were loose.
 
If the flicker affects table lamps plugged into socket outlets, maybe next time the fault occurs, switch off the lighting ccts via their MCB's and see if the flicker on the table lamp stops?
 
when all else fails, call in:
5042bd1991ba3f02752dcff392c183a0.jpg
 
Apologies if you've already given this detail - how often is the dimming, how deep and duration?
I love a fault - much more interesting than TV :)
 
Apologies if you've already given this detail - how often is the dimming, how deep and duration?
I love a fault - much more interesting than TV :)

Hi there.

It’s hard to answer with specifics. I’ve noticed it pretty much daily - at different times of day and no real set interval between.

The dimming itself is almost like a blink. It’s not what I’d call a flicker - it’s more a flash. Imagine looking at a light and blinking while doing so - it’s very quick.

I can’t really think how else to describe it.

Sometimes I’ve noticed it two or three times in a 10/20 minute period, other times I’ve not noticed it at all in the same time span.

It’s frequent and obvious enough to be a concern to me though.
 
These questions have maybe been answered before.
Do the lights flicker in unison across all the circuits? Have you tried a table lamp in an alternative socket ie, cooker unit? Still flickers?
If it does, it must be something common to all circuits, such as the supply. If this only started happening after the CU change, then very possibly a loose connection on something that has recently been worked on.
Have ALL connections been retightened? even the factory fitted? (Neutral link between mainswitch and neutral bar?)
It is very easy to misalign the busbar when fitting MCB's. It can sometimes slip up behind the clamp of the breaker, and tightening up the connector screw makes no difference.
Working on the CU tails may have loosened them at the meter just by moving them around. Not something your electrician can check if the seals are still in place.
How does the supply cable come into the house? Overhead wires can give problems, but of course that's up to the Network to check.

We would all be interested to find what the problem is once its been identified.
 
Reverse polarity!! Energy savers

Politely disagree.
I don't think it would be reverse polarity. The OP said it was ceiling lights as well as table lamps. Likely to be bayonet cap fittings - doesn't matter which way round they're put in... and also said it happens with filament lamps... not 'energy savers' in the sense that if they are CFL or LED.
And between the electrician, his return visit and the ones that came to check the supply, someone would have visually noticed the cables being reversed between the meter and the CU.
 
Politely disagree.
I don't think it would be reverse polarity. The OP said it was ceiling lights as well as table lamps. Likely to be bayonet cap fittings - doesn't matter which way round they're put in... and also said it happens with filament lamps... not 'energy savers' in the sense that if they are CFL or LED.
And between the electrician, his return visit and the ones that came to check the supply, someone would have visually noticed the cables being reversed between the meter and the CU.
I should say that it has been noticeable on LED GU10 bulbs, and also on the old energy saver types (not LED - the ones that looked like small tubes in a loop). It was just more noticeable on the filament type bayonet bulbs. I’ve replaced all them filament types with LED bayonets now and it’s no longer noticeable on those lights, but is still happening on the GU10 bulbs in the kitchen, bathroom and bedroom.
 

Reply to Advice ref blinking lights all circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
630
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
648
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
721
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
900

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock