J.C.E

-
Arms
Reaction score
158
Just going through my EIC that i will be summitting to BC- then to use this job for my Niceic initial assessment- so just trying to make sure theres no holes!

job is just new ring circuit to 2 sockets out a 32a mcb on 30ma rcd side of a existing 16th board.

in sec 3- comments on existing installation

i have put 'unable to verify charactoristic of primary over current protective device- suppliers property'
-them put LIM in section 8 for supply protective device.
and 'incoming water main is plastic on supply and consumer side of stop cock- recommend installing bonding to 1st point of copper pipe where reasonably practical.'

in sec 6- any departs

i have put 'absence of circuit schedule for fuse board (c3) Absence of testing and inspection notice (c3)'
 
Dave beat me to it!!!
 
And the assessor will probably be wondering why you would run a ring to serve just two sockets as it suggests a lack of design ability/knowledge.


Originally plan it to be a radial as you say its only 2 sockets

then it was decided thermal insulation was being used in the stud- changing my ref from c to 103!

instead of buying bigger cable 4/poss 6 i decided to keep the 2.5, do it as a ring and have 20a as ocd

ccc for 2.5 in 103 is 13.5a x2 (ring) 27a

thats why its a ring


if i was to leave as a radial as ref 103- ccc would of been 13.5amp and would of had to go on 10amp ocd


made the best out of a bad situation that i couldnt help!

if i explain the above with conviction- will that not show competence?
 
You are not allowed to use 'LIM' on an EIC

I see that this has been debated before on this forum . I note that reg 634.2 (referring to limitations) is only under 634 Periodic Inspection & Testing. I've looked through GN3 (green version) and can't find the reference to not using 'limitations' in an EIC.

Using the online certification provided by Elecsa (think niceic use exact same software by Certsure), the only selectable option for rated current for the primary supply OPD is, either the rated current (i.e. 100a), N/A or LIM. It won't allow you to put anything else in there. 'LIM' is also an option for all the other characteristics for the primary supply OPD.

'LIM' is also an available option in the 'test results' section.
 
No there's no reference to not using LIM, just as there's nothing stating you can't use a 6" nail as a fuse.
BS7671 is a standard, not a list of what not to do or a how to book.
 

Reply to Advise on my EIC to be used on niceic assessment in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
11K
NICEIC Certification Scheme Newbie & NICEIC assessment advice!
Hi all, Newbie from the West Midlands, just starting out in the electrickery world (certainly not in life... change of direction) and have my...
Replies
13
Views
4K
NICEIC Certification Scheme interesting convo with NICEIC today
Had my annual visit today, passed so all good. Discussed when exactly i was meant to have the 18th edition, he said that actually i didnt need to...
Replies
11
Views
2K
NICEIC Certification Scheme First NICEIC Assessment
Hello, Ive got my first NICEIC Approved assessment coming up with Tim Leibe. Ive been with Elecsa in the past but decided to go for the full...
Replies
6
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock