Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance "engineer" to commission Heat-Pump, as original company disappeared before installation. ASHP worked for a while then tripped the 100mA RCD not the 30mA. Both RCDs tested at nominal trip current and ramp test.....both passed. Selectivity obviously working fine. The supply works with a 3KW kettle and will operate with the ASHP if the earth is disconnected at the ASHP.
There is a very healthy earth to the DB.

Theories and similar experiences appreciated...........................
 
Has anyone tested the Earth leakage current at the ASHP and also at the D.B / C.U it's fed from?
What else is fed from the Local board with the 100ma S type?
 
Snowhead beat me to it - typing too slowly!

Sounds like the ASHP has developed a leak to earth. Moisture somewhere?
Have you IR tested the circuit and pump?

Sorry no similar experience - my leak was glycol not electrons 🤫
 
Hi Thanks for your input. There is a workshop and stables fed from the same protected circuit. This was the first point of call and the circuit was isolated (double pole) with no effect on the outcome. The AC side of the solar array was also isolated even though this is fed into the main phase blocks through its own DB. Earth leakage at the DB was 3.1mA, I did not test the ASHP as I presumed that would be part of the "engineer's" procedure. Ramp test for the 100mA S type RCD 72mA, and for the 30mA was 21mA. Supply cable between 100mA RCD and DB was clear and fine.
 
Well I thought that your comment that disconnecting the earth from the ASHP allowed it to run was very significant.
I don't have any suggestions as to why the 'wrong' RCD tripped!
But I think that is secondary to finding the cause of the problem.

ASHP can generate a lot of condensate, depending on how hard its working and relative humidity, although at this time of year not so much. I was just wondering if earth leakage could be self-inflicted by the ASHP on itself! Eg because of a drainage problem for example.
 
Well I thought that your comment that disconnecting the earth from the ASHP allowed it to run was very significant.
I don't have any suggestions as to why the 'wrong' RCD tripped!
But I think that is secondary to finding the cause of the problem.

ASHP can generate a lot of condensate, depending on how hard its working and relative humidity, although at this time of year not so much. I was just wondering if earth leakage could be self-inflicted by the ASHP on itself! Eg because of a drainage problem for example.
I am totally with you on that Avo. It makes no sense as the supply cables are all sound. I am hoping someone sees this who has had the same experience. All I can think of is the 100mA RCD has been damaged in a way I have never seen. It tests fine. It is an AC type as it was installed in 2018. Some HVAC guys I spoke to say they specify B Type RCDs as matter of course and that should come from the manufacturer or engineer. Although these RCDs deal more with "DC-blinding" where as in this situation, not tripping is not an issue.
 
I suspect the ASHP's inverter circuitry and associated EMC filter are producing an earth leakage current which may extend to higher frequencies than the mains 50Hz. The first thing to do is look at the ASHP's installation manual to discover what type of RCD is required. Please post full details of the ASHP so we can look up too. A quick way to find out would be to phone the ASHP manufacturer's technical help line.

Here is a short article which gives an introduction to what I suspect is happening:

Heat Pumps – Type F or Type B RCDs? - Electrical Contracting News (ECN) - https://electricalcontractingnews.com/news/heat-pumps-type-f-or-type-b-rcds/

I am not at this stage by showing you the link saying that the solution is a Type F or Type B - we need to look at the manual or contact the manufacturer first.

Note also that one cannot place a Type F or Type B downstream of a Type A or AC so it is likely your ASHP may need a dedicated supply taken from the meter output.
 
Last edited:

Reply to Air Source pump tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
671
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
Replies
0
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
903

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock