Discuss Alterations to an installation with a 1980s (?) Wylex board protected by a single external RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
2
Just carried out a pre-work survey (older property and I wanted to check it over) for a client that wants a few extra sockets and other bits and bobs. The installation has a 5-way Wylex board (I’m guessing 1980s - white/cream plastic) which has had RCD protection added externally at some point - so the entire installation us protected by the single RCD. Circuits are: water heater (no longer used for immersion), sockets (combined ring for downstairs and upstairs), lights downstairs, lights upstairs), and cooker. Earthing and bonding, Ze both fine. R1+ R2 on upstairs lighting intermittent - some roses without earths. Older imperial cable but IR tests L-N > 500, L-E > 500, N-E > 8 (suspect neutral caught or similar). If I add additional sockets, my work has to be compliant, but the single RCD plus the single ring clearly don’t comply with section 314 (division of installation)… What's the general feeling here? The client has only just purchased the property and is not cash rich... Ideally it would a new CU (plus remedial work as appropriate) but if I can remain compliant without that the client would prefer it.

Thoughts?
 
FWIW I would make the changes but comment on the MWC about the single upfront RCD....

There are people still installing single rcd boards today
 
Your work has to be compliant. You're not adding the upfront rcd so the division of installation issues are not part of the work you are carrying out.
Your cert should reflect the scope of works covered by it.
 
There is a single non compliance, which does not cause danger but could cause inconvenience but not very relevant to a domestic property, in the existing installation.
If you are completing minor works then you are certifying that you have not made the installation worse in compliance and that your addition is compliant with current regulations.
I would recommend that improvements could be made and should be planned for in the near future, but I would have thought the current planned work could go ahead.
 
Division of circuits is not major issue. Its not going to be left any worse after you have added a few bits. Out radstock near bath a lot of the small houses have 1 circuit for sockets. 1 for lights. 1 for cooker and one for immersion or a boiler. Houses so small it doesnt need more.

As for missing cpc on lights. Not uncommon around our parts. Stick with class 2 fittings.
The electrical safety first best practice guide for light circuits without a cpc / changing cu gives some useful info
 
Yes, it is funny I live in a road of ten houses built in the early 70s. Ours is all metric cabling (1.0 cpcs in the 2.5 cables) but up the top of the road where the building started so I am told, the cables are a mix of imperial and metric!
 
thankfully, we are leaving the EU before the cretins make us drive on the wrong side of the road. wishful thinking now is :

1. back to feet and inches.
2. stranded T/E as in 7/029, 3/029, etc.
3. Red/Yellow/Black.
4. £.s.d.
5. acts of parliament to outlaw political correctness and erase the word "gender" from the English language.
 
Division of circuits is not major issue. Its not going to be left any worse after you have added a few bits. Out radstock near bath a lot of the small houses have 1 circuit for sockets. 1 for lights. 1 for cooker and one for immersion or a boiler. Houses so small it doesnt need more.

As for missing cpc on lights. Not uncommon around our parts. Stick with class 2 fittings.
The electrical safety first best practice guide for light circuits without a cpc / changing cu gives some useful info
Do people actually consult these Best Practice Guides, do you really carry one about?
 
Do people actually consult these Best Practice Guides, do you really carry one about?

Don't carry them BUT as they are written in "plainer" English than the BYB they are easier to understand, there are fewer interpretations and therefore easier to remember ............

You could download them onto your mobile if you wanted!

The IET could learn A LOT by reading them and / or employing the people that write them!
 
My parents house was built in 74. same age as me, and it has solid cores in the T&E.... and that's T with an E... not just T on its own.
So I think your estimated age is a little on the young side.

Asking some of the older gentlemen on here, was there a changeover period in the regs when imperial changed to metric sized cables?
Like when the harmonized cable colours came in, we had 2 years to use up the old stock.
 
change from imperial cableto the solid metric rubbish was early 70's, iirc
 
My parents house was built in 74. same age as me, and it has solid cores in the T&E.... and that's T with an E... not just T on its own.
So I think your estimated age is a little on the young side.

Asking some of the older gentlemen on here, was there a changeover period in the regs when imperial changed to metric sized cables?
Like when the harmonized cable colours came in, we had 2 years to use up the old stock.
But you weren't supposed to mix the two in a new installation,well that's the rule by I went by at the time we were doing blocks of flats so I ordered loads to complete the ongoing block and new colours for blocks onwards.
 
Thanks all for your input. I guess the key reference is from p. 116 of the Sparky's Guide to the Building Regs, that states:

"1.6 Regulation 4(3) states that when building work is complete, the building should be no more unsatisfactory in terms of complying with the applicable parts of Schedule 1 to the Building Regulations than before the building work was started. Therefore, when extending or altering an electrical installation, only the new work must meet current standards. There is no obligation to upgrade the existing installation unless either of the following applies:
(a) The new work adversely affects the safety of the existing installation.
(b) The state of the existing installation is such that the new work cannot be operated safely."

The L/N were both 7/029 with the CPC 3/029. I've attached a snap of the board, it's similar to some of these Wylex Standard white plastic fuseboxes - https://www.flameport.com/electric_museum/wylex_fuse_boxes/wylex_standard_white_plastic.cs4

View attachment IMG_0152.JPG
 

Reply to Alterations to an installation with a 1980s (?) Wylex board protected by a single external RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
642
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock