Discuss Am i able to do this to get zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

F

Flakey

I have a fused spur which is for an immersion located in a cupboard. the problem is i am not able to remove the front of the spur to get a ZS reading due to the location of the spur. in the cupboard is a socket which is part of the ring circuit am i able to put a probeon the live in the socket and put the other probe on the screw of the fused spur (taking that it has a cpc connected to it) and use that reading. or do i have to use the same live as well as the earth of the same circuit?

Many thanks

James
 
years ago that was a method used, today it is illegal and the modern testers won't allow a plug top lead and a trailing lead to be used together, my view would be if the spur is inaccessable it needs to be moved.
 
why not get your reading from the terminals on the immersion heater itself? this will prove that the cpc is continuous to the tank.
 
years ago that was a method used, today it is illegal and the modern testers won't allow a plug top lead and a trailing lead to be used together, my view would be if the spur is inaccessable it needs to be moved.
Hi there and thanks for your reply.
I was going to unscrew the socket and use probe leads i.e brown probe on live termination screw of socket. and green probe on screw of spur. So would not be use plugtop lead.
I hope i understood your answer correctly
and thanks again
 
top of the heater can't be that awkward or else how do you get it out if it needs replacing?
 
still not the way to do it though fella, My inspecting engineer would give birth if he saw me do that.
So the live/ live and neutral of the same circuit must be used in conjunction with the cpc to get a true ZS reading for the circuit. Nice one i just pressumed i was looking for the earth path alone but needed lives to make my tester work. obviously i would only use the same circuit conductors but due to the circumstance thought i may be able to wrangle it :) cheers!
 
Mate you are testing the Zs of an immersion circuit. If you use the live of an adjacent socket circuit along with the earth of the immersion circuit it will never in a million years give you the Zs result for the immersion circuit. It might prove that you have a CPC at the immersion spur but then again so would an R2 using a wander lead. As Tel says test it at the immersion element.
 
Mate you are testing the Zs of an immersion circuit. If you use the live of an adjacent socket circuit along with the earth of the immersion circuit it will never in a million years give you the Zs result for the immersion circuit. It might prove that you have a CPC at the immersion spur but then again so would an R2 using a wander lead. As Tel says test it at the immersion element.
Thanks for your reply mate i was asking because i did it and got a zs reading on my tester but wanted to know if the reading was a valid Zs reading cheers!! Zs = Ze + r1 + r2 :)
 
whichever way you can do it, as long as you know that the points you read from give a true indication . e.g. you could have a cpc at the socket, but not necessarily at the FCU. it could be loose or disconnected. that's why i suggested measuring at the heater itself. then you know it's intact to the point of use.
 

Reply to Am i able to do this to get zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
692
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket, I was gonna put the socket behind...
Replies
3
Views
600
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
643
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock