Hi Guys and Gals, currently I am finishing off my NVQ & i'm being asked the question on One file "Check the safety of electrical systems prior to the commencement of inspection, testing and commissioning".... Is this just fancy wording to say check Ze before you do anything else?
Any advice with this would be great... Cheers me lovers!
 
I would expect that this is referring to the requirements to ensure that that the existing installation is adequate for the addition or alteration you are installing (132.16) and so would require the information and details covered in 132.2 to 132.5.
However as they are stating that this is required before inspection testing and commissioning, but do not state it is required before design and installation I am somewhat at a loss as the assessment of supply characteristics should be done prior to design or you cannot plan the installation.
 
Thanks Guys, you have provided some clarification on this. I have looked at 132.2 to 132.5 & 132.16.
So as I understand a visual inspection of the supply to ascertain its characteristics (TN-S, TN-C-S, TT) along with a Ze to confirm presence of DNO's earth and test the bonding (once disconnected as to remove parallel paths) with a wondering lead.
 
I would think that to ensure safety before inspection, first off would be to verify the installation or part of the installation being inspected is de-energised.
Second would be to verify continuity of earth conductors and the presence of earthing.
and bonding.
 
Agree with the above post as if you read the OPs post it states Check the safety of electrical systems prior to the commencement of inspection, testing and commissioning"... The commissioning being energising a circuit or circuits.
 

Reply to Am I being asked for a Ze reading before any work? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
780
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
464
Hello, I am asking for a double check on my project before I purchase any electrical parts. My inverter Solark 15k has a built in 200 bus and...
Replies
0
Views
799
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock