For reference these are the Zs tables from BS7671 Amendment 3, provided by Amberleaf.
I have cleaned up the scans a bit which is why they may look a bit odd round the edges.
Regulation Table(2) 41.1.jpgRegulation Table(2) 41.2.jpgRegulation Table(2) 41.3.jpg
Regulation Table(2) 41.4.jpgRegulation Table (2) 41.6.jpg

Remember IET have also issued the corrected tables for the latest GN3 page 121 table A4 and OSG table B6 which are available for free download here .
 
Hi Richard

Cheers to you and Amberleaf for your efforts I am just in he process off finding somewhere to purchase the new books without having to give them an arm or a leg lol

regards
 

Reply to AMD 3 Zs tables and GN3 and OSG corrected tables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Getting out of the game and want to get rid of these as i don't need them anymore. Paid £174 for the BS7671, OSG + GN3 bundle and £22 for the T&I...
Replies
3
Views
1K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Hi, as an aspiring sparky I'm needing help with the temperature adjustment formula for Zs. I'm using GN3 (17th). I understand that the values...
Replies
3
Views
2K
On page 142 of the latest Guidance Note 3 it list a 16 amp type B max ZS as 2.15, however i think 2.2 is the real value, it also states that at 16...
Replies
15
Views
5K
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock