Discuss Anyone have American electric questions? in the USA Electrical Forum area at ElectriciansForums.net

That's funny, ...every US GFI breaker or GFI receptacle i've come across, and that a considerable amount, have always been clearly marked for 6mA!!!

Haha... we have a range of RCD devices, some come in an S type version, (time delayed) 10mA, 30mA, 100mA, 300mA, 500mA
We in Europe tend to protect complete circuits with RCDs, whereas accross the pond there, you tend to protect a load/appliance via a RCD receptacle, or a GFI breaker circuit with a specific single load. Imagine the level of nuisance tripping on for argument's sake, a receptacle circuit with an RCD breaker trip level of just 6mA!! lol!!

Also we ensure that installations are limited to having a maximum touch voltage of 50 volts, so that they are not lethal. ...lol!!! The easiest way of explaining that to you, is maximum values of ground rod protected systems linked to RCD devices. (As the states use a hell of a lot of TT systems ''Ground rod grounding'') So U =RI, say R=50v/0.3A (300mA) =167 ohm Max, ....or R=50v/0.1A (100mA) =500 ohms Max. I'll let you do the calc for a 30mA RCD...lol!!

Hope that makes some sense to you, as i'm not concentrating to well, ... i'm doing other things at the same time here at the moment...lol!!!
 
yes, we mostly use what you call TT systems. think about this: A= v/ohms. for 120v and maximum allowable ground of 25 ohms, 5 amps flow and the 20 amp breaker wont trip.
But the 5 or 6 mA gfci will, so lethal shock is prevented. in a British system, 30mA RCD, you would be dead.
 
Is an Electrician considered a decent tradesmen job in the USA, from what I heard the construction industry over there is very badly paid, or have I been told porkies?
 
Yes, an electrician was a decent tradesman job in the States. But now with the global depression, our salary is only 50-60%
what it used to be, and thats if you can get work. Unemployment is sky high, especially in construction. I get an email from ppl I used to work with saying "Im not working and I dont know anyone who is." Which explains why I work in the mid-east, there is no work in the States. Hopefully, when normal economic times return, electricians will go back to getting decent wages like we always used to :)
 
yes, we mostly use what you call TT systems. think about this: A= v/ohms. for 120v and maximum allowable ground of 25 ohms, 5 amps flow and the 20 amp breaker wont trip.
But the 5 or 6 mA gfci will, so lethal shock is prevented. in a British system, 30mA RCD, you would be dead.

Really ??? we were taught that 50mA is the lethal limit (granted it will vary depending on the person)
 
How's it goin lads,don't use this forum much,this is my first thread.Gona start using it much more now.Anyway,Im a spark from N.I looking for work in either Afghan or USA.I was told that a British certified electrician would not be recognised in USA,and that I would have to apply for an apprentice journeyman's state licence,taking up another 4 years! Is this true?
This info was given to me by a fellow user on Flour corp's logcap forum,who is himself a (USA) journeyman working in Afghanistan.I found it hard to believe,I expected an update course of some discription.
Any opinions or info would be appreciated.cheers lads
 
licensing in the states is in control of each individual state, and each states sets its own rules. you just have to check with the state u want 2 go to. btw, theres lots of UK electricians working in Afghanistan, Iraq, etc. Your 17th ed license is the only thing u need in
British bases, Afghan Army or Police bases, etc.
How's it goin lads,don't use this forum much,this is my first thread.Gona start using it much more now.Anyway,Im a spark from N.I looking for work in either Afghan or USA.I was told that a British certified electrician would not be recognised in USA,and that I would have to apply for an apprentice journeyman's state licence,taking up another 4 years! Is this true?
This info was given to me by a fellow user on Flour corp's logcap forum,who is himself a (USA) journeyman working in Afghanistan.I found it hard to believe,I expected an update course of some discription.
Any opinions or info would be appreciated.cheers lads
 
yes, we mostly use what you call TT systems. think about this: A= v/ohms. for 120v and maximum allowable ground of 25 ohms, 5 amps flow and the 20 amp breaker wont trip.
But the 5 or 6 mA gfci will, so lethal shock is prevented. in a British system, 30mA RCD, you would be dead.

Where do you keep getting this ''lethal'' shock thing from?? 30 mA is the threshold of heart fibrillation!!! It's not just the UK that use this level in RCD device (GFI) protection, the whole of Europe uses it too, along with most of the Middle and Far East. Coming back to the UK/Europe for a moment, we also have very stringent disconnection times for different levels of leakage current that may pass through an RCD, that all RCD devices MUST meet.

If you were even partly correct in your idea of ''30 mA and your dead'' theory, we could be talking about millions of casualties, ....but alas as your so wrong, there isn't and never has been!!! Maybe talking to a UK or European electrician where your working in the Middle East can explain more about our RCD regulations along with the 50 volt touch voltage limitations many of our circuits must also comply too...

Your NEC doesn't call for, or state a ''maximum'' rod Ra of 25 ohms. It notes a stated recommended value, and if that value cannot be obtained with a single rod then another rod must be provided. Your not even required to test the second rod, or the combined value, as according to the NEC, providing the second rod fulfills obligations...
 
Your NEC doesn't call for, or state a ''maximum'' rod Ra of 25 ohms. It notes a stated recommended value, and if that value cannot be obtained with a single rod then another rod must be provided. Your not even required to test the second rod, or the combined value, as according to the NEC, providing the second rod fulfills obligations...
Correct! Which is why the customer many times calls for ground rings in their installations. The NEC sets minimum standards only.
Our inspectors [my installs are inspected by 3 organizations] set their own spec over and above the NEC minimums. Engineer54, thx for your posts, I always learn from them :)
 

Reply to Anyone have American electric questions? in the USA Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Sticky
We have got some other sections of the forum that I thought might be useful to you guys! They are for all countries but we have new tags that you...
Replies
0
Views
721
I`d just like to say hello to everyone, all site owners,regulators and all contributors . I have used these pages for a while now to look for...
Replies
1
Views
217
Great to be joining such a supportive and interactive forum. Should anyone have any questions about my company or the products we sell just give...
Replies
1
Views
266
N
Like another post a few minutes ago, I have been asked to post a new thread to keep my membership of this forum and I'm sorry if this clutters up...
Replies
1
Views
131
  • Sticky
  • Article
ANNOUNCEMENT: New Moderator Assigned: @Megawatt (Please congratulate!) @Megawatt has been a forum member for a while now, he's an American chap...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top