Just looking for a bit of clarification regarding RCD's.

A type AC RCD is no longer acceptable for offering additional protection for socket outlets. If you are (for example) adding one socket to an existing circuit are you all updating the RCD to a type A? I can see this being a bit tricky sometimes. It's ok if its a brand of consumer unit that does type A RCD's but this will not always be the case.

Do the regulations mean that if you are extending an existing socket circuit you cannot use an existing type AC RCD?
 
I think it would depend on the circuit or circuits & what equipment the RCD is protecting. I guess changing it will cover further additions or changes of equipment that would need DC protection.
 
Last edited:
Technically yes, it should be replaced, it's no different from before, if you needed to add an additional outlet or circuit, and the existing protection wasn't up to spec you would change the existing, or add something such as a rcd where there wasn't one previously.

It isn't something I quite agree with as there are always circumstances where this ups the price beyond what the customer is willing to pay.

For example, grandson finds granny fallen due to tripping over an extension lead (for the Xmas tree), so suggests adding a socket near the corner where the tree goes, - but, it needs rcd, none available for the existing cu etc - basically a single socket results in a new cu etc.

The end result is that nothing gets done to improve the situation, and granny goes back to using and tripping over extension leads!

I do sometimes think the distance we have to go in order to be compliant is a bit too far at times, I would much rather a half way there improvement to none at all - although of course we have to make sure this isn't abused
 
I think I may use a degree of common sense.

If I am able to change the existing type AC to a type A (fairly easily) I will factor this into the quote.

If it means a board change I may choose to give them that as an option rather than make it mandatory.
 
Last edited:
You could always list it as a departure on the certificate. Not great but I think for a small job, the addition of a socket etc its okay, as long as you have offered the RCD change
I used to think the departures box was for this sort of use (ie get out of jail free). However, thanks to one @davesparks posts I realise this is not it's intended use.

The departures box is simply if you have done something that departs from BS7671, but (and this is the crucial bit) "The resulting degree of safety of the installation shall not be less than that obtained by compliance with the regulations" (120.3)

It would be less safe by using a type AC than a type A, so this isn't suitable for the departures box.
 
Same with all BS, if you depart from the content of the BS it must be to go "above and beyond" the requirements in that standard, this is quite clear from the HSE and has been tested in Court on a number of occasions.
 
If replacing the device in the CU isn’t viable then I suppose changing a point on the ring for an RCD spur for the addition is a possibility now they are back in the regs.
Of course, either/both may trip but no one can say the addition doesn’t comply with latest regs.
 
I used to think the departures box was for this sort of use (ie get out of jail free). However, thanks to one @davesparks posts I realise this is not it's intended use.

The departures box is simply if you have done something that departs from BS7671, but (and this is the crucial bit) "The resulting degree of safety of the installation shall not be less than that obtained by compliance with the regulations" (120.3)

It would be less safe by using a type AC than a type A, so this isn't suitable for the departures box.
Yes, I agree.
I was just thinking what could/would i do. This is going to be something we will all have to deal with over the next few years
 
I absolutely replace with A type RCBO. In fact you can't really get any other now. But aside from regs, if something can produce a safer installation then of course use it. I am a bit concerned that places like screwfix, b&q are selling dual rcd cu at pretty cheap prices. Recently I was asked to do a cu installation and the guy had bought two dual rcd which were the old AC type and I said he would have to take them back and get a refund as they don't meet regs now. I wonder how many have a go DIY are fitting these. And should such stores even be selling them. It does seem rather irresponsible of them to do so.
 
New posts

Reply to Are you replacing type AC RCD's with Type A? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
853
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
970

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock