Discuss Asbestos behind 3036 fuses solution needed? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
6
What coding would you be giving for old DBS with asbestos behind fuses? As its not affecting electrical safety?
is there something you can put in place of the asbestos when removed, as its to hold in arcing or flashing when the fuse wire blows right?
if you remove the asbestos does this then make the db equipment to be installed against manufacturers requirements?
 
Should it not be removed ,pulling the fuse creates dust, even a minimal risk is a risk and if your pulling a 1000 minimal risk fuses that will make the minimal risk greater surely?

The old boy's like myself have probably pulled many 1000's of these fuses, they are still here to tell the tale!! Hell it was one of my jobs as an apprentice to go round during our factory shutdowns replacing the glazed asbestos wading behind the fuse carriers cutting from different width rolls of the stuff.

Only the other day i suggested to another poster here, that if you're that concerned about pulling a 3036 fuse, pass the job on to another qualified electrician that hasn't surcomed to all the scaremongery that surrounds these old fuse boards that contain asbestos flash guards....
 
having smoked 20 -30 king size smokes a day for 50 years, i don't think a few crummy asbestos flash guards can do me any harm. LOL.
 
Its an expensive and professional job to have the asbestos removed, you shouldn't be removing it yourself as you will need to be licensed to dispose of the asbestos.
The dust you see when you pull the fuse carrier out is more then likely from some other source and not from the flash guard / asbestos which has sat there happily for many years.
 
Electricians that have developed asbestos related lung diseases, have in the most part been subjected to airborne blue or grey asbestos dust while working in or around laggers, during buildings construction. The most dangerous being the area they were mixing the product prior to installing the layers of lagging to pipes and ductwork etc.....


Trying to say that these tiny bits of glazed white asbestos flash guards represent anywhere near the same danger level, is frankly taking the Pee. Not saying that you shouldn't be careful or not use commonsense, but pulling a fuse (or several fuses) ain't gonna kill you in 30 years time either!! lol!!
 
I was a toddler of about 3 years old when Mum had an ironing board.

It was made from wood and folded up when it was not in use. There was a shelf thing on the end to rest the iron on and this shelf thing had a pad of asbestos.

When the board was not in use it was folded up and leaned against the kitchen wall, the asbestos pad was at the perfect height for me to pick and scratch bits off it and try to eat it.

Then there was my hobby of Model Engineering where I made model steam engines with asbestos lagging on the boilers and asbestos gaskets on the cylinder and valve chest covers - all cut from asbestos sheet by hand.

I am now well on the wrong side of 60 years old but I'm still here.

My Mother's uncle on the other hand worked as a lagger in the power station and worked with large quantities of the stuff day in and day out. He died of cancer aged about 70.

I do not think the relatively small amount found in fuse boxes is going to do much harm.
 
Remember that all asbestos is dangerous, the difference between white, blue and brown is not really a significant issue as it can take just one asbestos fibre to cause problems.
Yes blue and brown have more spiky fibers and so have more chance of getting caught in the lungs than being expelled but any fiber could lodge in the lungs.

That said the risk from undisturbed asbestos is minimal, the flash guards being a case in point.
To remove them would generate far more risk than leaving them in place.
Any reasonable risk assessment would include procedures for not disturbing the flash guard in normal use but should not recommend removal unless the equipment is being decommissioned.
 
Remember that all asbestos is dangerous, the difference between white, blue and brown is not really a significant issue as it can take just one asbestos fibre to cause problems.
Yes blue and brown have more spiky fibers and so have more chance of getting caught in the lungs than being expelled but any fiber could lodge in the lungs.

That said the risk from undisturbed asbestos is minimal, the flash guards being a case in point.
To remove them would generate far more risk than leaving them in place.
Any reasonable risk assessment would include procedures for not disturbing the flash guard in normal use but should not recommend removal unless the equipment is being decommissioned.

Agreed

Very sensible.
 
Remember that all asbestos is dangerous, the difference between white, blue and brown is not really a significant issue as it can take just one asbestos fibre to cause problems.
Yes blue and brown have more spiky fibers and so have more chance of getting caught in the lungs than being expelled but any fiber could lodge in the lungs.

That said the risk from undisturbed asbestos is minimal, the flash guards being a case in point.
To remove them would generate far more risk than leaving them in place.
Any reasonable risk assessment would include procedures for not disturbing the flash guard in normal use but should not recommend removal unless the equipment is being decommissioned.


Sorry, but there ''IS'' a significant difference in the types of asbestos related to death and disease. If you have attended one of these Asbestos Awareness courses, they make that aspect very clear.
 
Sorry, but there ''IS'' a significant difference in the types of asbestos related to death and disease. If you have attended one of these Asbestos Awareness courses, they make that aspect very clear.

I agree that blue and brown asbestos have risk levels an order of magnitude above that of white asbestos in terms of levels of exposure to the correct lengths of fine particles and that the identified risks from white asbestos are not fully quantified.
However it is fairly certain that a risk is still present for the white asbestos to cause lung problems, though generally at high concentrations of exposure.

Because that risk is present and because it is not possible to tell without analysis the type of asbestos and therefore if there are contaminants of the other types of asbestos (dependent on the source of the mineral) it is better to assume that "asbestos" in general does have a risk factor and to handle the material appropriately without taking account of the actual type, if you are considering asbestos from a layman's point of view.

However since the risk factors from undisturbed asbestos, i.e. there are no fibres present in the air, is at an absolute minimum there is no need to take extreme measures. prevention of the release of fibers is the best way to limit the risks.
Exposing asbestos removal workers to additional risk by removing the material and also presenting a potential risk to later occupants / users of an area should the containment not have been complete at the time of removal does not seems to me to be a good idea.
 
I agree that blue and brown asbestos have risk levels an order of magnitude above that of white asbestos in terms of levels of exposure to the correct lengths of fine particles and that the identified risks from white asbestos are not fully quantified.
However it is fairly certain that a risk is still present for the white asbestos to cause lung problems, though generally at high concentrations of exposure.

Because that risk is present and because it is not possible to tell without analysis the type of asbestos and therefore if there are contaminants of the other types of asbestos (dependent on the source of the mineral) it is better to assume that "asbestos" in general does have a risk factor and to handle the material appropriately without taking account of the actual type, if you are considering asbestos from a layman's point of view.

However since the risk factors from undisturbed asbestos, i.e. there are no fibres present in the air, is at an absolute minimum there is no need to take extreme measures. prevention of the release of fibers is the best way to limit the risks.
Exposing asbestos removal workers to additional risk by removing the material and also presenting a potential risk to later occupants / users of an area should the containment not have been complete at the time of removal does not seems to me to be a good idea.


At the end of the day here, were talking about pulling 3036 fuses in order to conduct a PIR (or whatever they call it now) So no need to touch or disturb the flash guard in anyway shape or form., why the OP is talking about removal/replacement i haven't a clue?

All i know is that, i wouldn't give pulling such fuses a second thought. You'll soon see if any extra care is required once the fuse has been pulled, ...rarely the case!!
 
I went on a abestos course at work, and never knew the fibres can stay in the air for a few weeks.
With the asbestos DBs, we have a clause in our LIMs that we do not open the asbestos DBs if we suspect presence
 

Reply to Asbestos behind 3036 fuses solution needed? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

An old and now deceased friend's place has some rewirable fuses with asbestos flash pads. They are long overdue for replacement and now that seems...
Replies
9
Views
770
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
I wonder if any one can give me some advice. I live in a fairly new build house it's 11 years old. In our kitchen there is a fused spur switch on...
Replies
18
Views
5K
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
694
  • Article
Electrical2Go - Save Time Installing Cables with Super Rod At Electrical2Go, we're constantly striving to bring you the latest and most...
Replies
0
Views
503

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock